Two transformers are connected in parallel out of phase then I assume the net voltage obtainable is the sum of the output voltages?
 
Last edited:

MaxHeadRoom

Joined Jul 18, 2013
28,702
Two separate transformers primaries are connected out of phase, they still require correct phasing of the secondaries if summed, either through prior indication of the relevant winding start or by detection.
If series connected, no harm can come of incorrect phasing, if identical windings in parallel, then incorrect phasing must be carried out or short circuit current is a result.
Max.
 

Thread Starter

bwd111

Joined Jul 24, 2013
117
Two separate transformers primaries are connected out of phase, they still require correct phasing of the secondaries if summed, either through prior indication of the relevant winding start or by detection.
If series connected, no harm can come of incorrect phasing, if identical windings in parallel, then incorrect phasing must be carried out or short circuit current is a result.
Max.[/QUOT
Or the net voltage obtainable is the same as if onre transformer was used or being used due to being hook up in parallel. Would you agree on that . I dont think it would be zero
 