    hi, i have a transducer , it is 24v in, 1-6vdc out.
    i wire the transducer to the power and check output with a multimeter and i get the .98v on the output leg, if i put the digital readout on gnd and the output leg it won't display. do i need a resistor inline? and if so what value, 10k?
    thanks
     
  2. strantor

    AAC Fanatic!

    Oct 3, 2010
    4,302
    1,988
    Transducer part number? Display part number? Quick draw a wiring diagram?
     
  3. bomrat

    Thread Starter New Member

    Dec 13, 2009
    25
    0
    hi, heres the drawing
    thanks
     
  4. shteii01

    AAC Fanatic!

    Feb 19, 2010
    3,376
    494
    The one time I worked with pressure transducer, the part info mentioned 5 kOhm or greater load, but I did not really pay attention because I had it hooked up to op-amp which by its nature has really high input resistance so I assumed that transducer was seeing a really large resistor load.

    Bottom line. Check transducer info for what it needs or contact manufacturer.
     
  5. strantor

    AAC Fanatic!

    Oct 3, 2010
    4,302
    1,988
    Transducer part number?
     
  6. bomrat

    Thread Starter New Member

    Dec 13, 2009
    25
    0
    keller pa=21sr transducer
     
  7. Dodgydave

    Distinguished Member

    Jun 22, 2012
    4,965
    743
    like this

    you need to put 5 bar pressure on it to get it to work.
     
    Last edited: Mar 26, 2014
  8. bomrat

    Thread Starter New Member

    Dec 13, 2009
    25
    0
    ok ill try that
    thankns
     
  9. strantor

    AAC Fanatic!

    Oct 3, 2010
    4,302
    1,988
    Where do you see that info? The datasheet for the PA21SR shows that it comes in several ranges from 1 to 600 bar. Overpressure limit for the 1 bar model is 3 bar. Hopefully OP will check his model/rating before applying 5 bar.

    It sounds like you're bench testing (no pressure applied to transducer) so .98V is correct and should be expected from a transducer with specified 1-6V range.

    Your drawing shows a two-wire "LCD readout 0-30VDC" meter from MPJA.com. I could not find a two wire digital meter on MPJA.com with those specs, and I seriously doubt that such a thing exists. A digital meter must have sufficient voltage to power itself before it can measure anything. It is more likely that you have one of the only (2) two-wire digital 30V meter models offered by MPJA; the larger 4.5-30VDC meters, in red, blue, and green, or the smaller 3.5-30VDC model in red, blue, and green.

    You need to be using a 3 wire meter like this.
     