I have been in contact with the supplier of the valves and received this reply -
Hello,
The valve do not need to provide power for all the time, you just need to provide it once they full open or full closed(3~4 sec)
Best Regards
Jimmy
Can you make sense out of that relay? I am not the best at Chinglish
Chinglish can be a fun and exciting language. Unfortunately at my age learning it just isn't in the plan. Been looking at something interesting though. In the small block diagrams of these valves they clearly show the motor and above the motor they show that block that is called control circuit. Since you have a few of these things here is what I suggest if you have a handy little DMM (meter). Use a 12 VDC supply and power a valve and in series with the valve measure the current. Once the valve reaches full travel in either direction see if the current stops? Just power the valve through the Yellow and Blue wires with a DMM in series with the load. If the current stops on full travel in either direction that tells us the thing does have and use limit switches not shown in the cartoons up to date and must be part of that control circuit block. That would make sense anyway. Like I said, when this stuff has data sheets they can be a puzzle to decipher. When they lack a data sheet it's anyone's guess.
Ron