StepDown Transformer forcing MCB to TRIP
Discussion in 'General Electronics Chat' started by BluePhantom, Nov 16, 2015.
  1. BluePhantom
    Nov 16, 2015
    20
    Hello
    I'm New to this forum..
    I decided to make a high power 25V power supply for running Mazzilli ZVS Driver.
    I got an old Microwave from scrap and took out the Transformer and removed the 2KV Secondary.
    I added new Secondary for 25V and Max. 40A, but when I connected the primary to AC Mains without any load on secondary
    the MCB tripped.
    What is causing the problem?
    Mains is rated 240V~ @50Hz
    Transformer is rated for MAX 1200W
    Thanks in Advance!
  2. MaxHeadRoom
    Jul 18, 2013
    10,827
    2,495
    You have a short on the new wound secondary.
    Max.
  3. BluePhantom
    Nov 16, 2015
    20
    I didn't short it but I tried to test the output with the multimeter..
    Also I have seen people who wind only 2 turns on secondary to use it as spot welder... There is a short too.,so why doesn't the circuit breaks in that case?
  4. MaxHeadRoom
    Jul 18, 2013
    10,827
    2,495
    What size is the MCB?
    Did you drive the magnetic shunts out?
    Maybe that was the reason the MW was scrapped in the first place?
    Max.
  5. alfacliff
    Dec 13, 2013
    2,449
    428
    did you remove the origional secondary windings?
  6. BluePhantom
    Nov 16, 2015
    20
    Mcb is rated for 20Amps
    Do you mean anything else by the size?
    shunts are still there..
    I also used a same mcb which was lying around as a switch with the transformer. But that didn't trip
  7. BluePhantom
    Nov 16, 2015
    20
    Please read and understand the question before replying
  8. MaxHeadRoom
    Jul 18, 2013
    10,827
    2,495
    After the initial inrush the current should be very low when unloaded.
    You could try a high wattage low resistance in series with the primary on initial turn on, short the resister after the short inrush period, if it blows the breaker, you have a short on the transformer.
    Max.
  9. crutschow
    Mar 14, 2008
    13,472
    3,361
    As a variation on Max's suggestion, you can put an incandescent bulb in series with the primary.
    If the bulb stays other than dimly lit with no load on the transformer it would indicate there's a short somewhere in the windings.
    MaxHeadRoom likes this.
  10. BluePhantom
    Nov 16, 2015
    20
    Is there a specific value for that resistor?
    Highest wattage in case of resistor I have 10w 500ohm resistors... Will it do?
  11. MaxHeadRoom
    Jul 18, 2013
    10,827
    2,495
    The lamp as in @crutschow post is better option, but you can try it, although if the transformer has a short circuit the resistor will heat up rapidly.
    Max.
  12. Dodgydave
    Jun 22, 2012
    5,138
    767
    Before you modified the transformer, was it working ok, whats the primary winding resistance?
  13. BluePhantom
    Nov 16, 2015
    20
    Yup it was working and giving 2kv output..
    Resistance is around 17.1ohms
  14. BluePhantom
    Nov 16, 2015
    20
    Yup I will try this..
  15. BluePhantom
    Nov 16, 2015
    20
    I was also thinking that resistor would burn away
    Is there any specific wattage for the bulb or i can use any lamp?
  16. Dodgydave
    Jun 22, 2012
    5,138
    767
    Try a 40 to 80w bulb, so what's the primary and secondary resistance now after modifications?
  17. BluePhantom
    Nov 16, 2015
    20
    Primary resistance is 17ohm
    Secondary resistance is 8.9ohm
  18. Dodgydave
    Jun 22, 2012
    5,138
    767
    Ok, maybe the primary winding is shorted to earth and that's causing it to trip, can you monitor the primary current with an ammeter?
  19. BluePhantom
    Nov 16, 2015
    20
    How can I do that if the circuit is broken just after turning it on
  20. Dodgydave
    Jun 22, 2012
    5,138
    767
    With the bulb in series with the primary winding, and no secondary load.
    Measure the resistance of both primary connections to earth one at a time.