i need the calculation for the amps for a star delta started motor, terminal box has 6 terminals so you are using 6 wires U1 V1 W1 / U2 V2 W2
eg if you have a 550 kw 400 volts wired in star delta what amps is that???
in star
current is
power(input)/(sqrt(3)*line voltage)--line voltage is voltage across two phases.
for delta:
there are two currents
current in each phase and current thru the supply lines,
power/(sqrt(3)*line voltage)
gives line current,
line current=sqrt(3)*phase current