    Hi I am trying to calculate the phase currents in a star connected un-balanced load.
    The phase voltage is 100V and the resistance in the yellow phase is 50Ω
    The formula I have is...
    100 ∠ -120°
    50
    I am struggling with how to input this into a calculator and how to get the amps in numerical value for the yellow phase.
    All help greatly appreciated - ElecNerd
  2. t_n_k
    Mar 6, 2009
    5,448
    783
    Your formula will be correct as long as the star point is tied to the neutral conductor and the voltage phase angle is -120° for "yellow" phase convention.
    As to entering the numbers using your calculator - you will need to study the user manual on how to do complex number operations.
    The calculation you have doesn't really require a calculator. The answer would be 2A @ -120°.