Snubber Diode

Thread Starter

qitara

Joined Jan 18, 2013
112
Hi Guys

I got a solenoid that is getting the relay that is driving it going bad due to the contacts getting welded, so now its time to install a diode across the solenoid, only thing is that I am not a pro at sizing the correct diode, So i would be thank full if some of you guys could help :)


the Solenoid is a 900W DC solenoid running on 110VDC.



P.S

If I change the Electromechanically relay with a SSR that has a load voltage of 0-400VDC and load current of 40 amp, will I still need to install the diode ?
 
Last edited:

GopherT

Joined Nov 23, 2012
8,009
Hi Guys

P.S

If I change the Electromechanically relay with a SSR that has a load voltage of 0-400VDC and load current of 40 amp, will I still need to install the diode ?
No, but check the manufacturer's DATASHEET and application notes to be sure of all requirements. I prefer the SSR option.
 

Thread Starter

qitara

Joined Jan 18, 2013
112
I prefer the SSR option.
Well I like the SSR option as well, but what I don't know is if it will run fine with the coil pumping current when its begin disconnected

if the solenoid causes the contacts on the electromechanical relay to get welded, what would it do to the SSR, will the SSR work fine without a diode across the solenoid ?
 

GopherT

Joined Nov 23, 2012
8,009
Check the manufacturer's DATASHEET. They will have recommendations (there may be a built-in diode or they may recommend adding one. Check it out.
 

Thread Starter

qitara

Joined Jan 18, 2013
112
checked the datasheet, but nothing was found there only the diagram showing a diode on the load side (terminal), I cant see how the diode will work when its not across the load ?
 

GopherT

Joined Nov 23, 2012
8,009
SSRs can handle AC or DC loads.

DC loads
This type of load should be considered inductive, and a diode should be placed across the load to absorb any surges during turn-off.
 

strantor

Joined Oct 3, 2010
6,798
The same current that flows through the coil will flow through the diode when the circuit is opened. So 900W/120V=7.5A. Your diode should be rated AT LEAST 120V/7.5A. Getting something rated a little higher than that wouldn't hurt.
 

THE_RB

Joined Feb 11, 2008
5,438
A coil diode won't stop the contacts being welded together.

You need an RC snubber across the coil contacts, to reduce arcing when the contacts open. Or a relay rated for enough DC contact current with your type of load.
 

crutschow

Joined Mar 14, 2008
34,423
A coil diode won't stop the contacts being welded together.

You need an RC snubber across the coil contacts, to reduce arcing when the contacts open. Or a relay rated for enough DC contact current with your type of load.
Au contraire. Don't understand why you say that. :confused: A reverse-biased diode across the coil will most definitely minimize the problem of the contacts being welded. The diode will carry the coil current when the contacts open, keeping the voltage transient voltage no higher than the forward voltage drop of the diode and essentially eliminating any contact arcing.

The transient voltage will be less than typically generated by an RC snubber. Of course the effect of using a diode is that it slows the release time of the solenoid as compared to an RC or zener diode snubber. So, if speed is important, you will want to consider using one of those instead.
 

strantor

Joined Oct 3, 2010
6,798
I also had beef with RB's statement, but I know who the bigger expert is. So assumed he was right and I was wrong. I wanted to do the digging and pull some references but I didn't have the time to find anything that spelled it out. So I'm glad you spoke up, let me know that my understanding isn't fundamentally wrong.
 

creakndale

Joined Mar 13, 2009
68
1500W Transient Voltage Suppression (TVS) Diode. Like this one from Littelfuse:
Part number: 1.5KE150A, Unidirectional, 1500W, Vr=128v

creakndale
 

ian field

Joined Oct 27, 2012
6,536
Hi Guys

I got a solenoid that is getting the relay that is driving it going bad due to the contacts getting welded, so now its time to install a diode across the solenoid, only thing is that I am not a pro at sizing the correct diode, So i would be thank full if some of you guys could help :)


the Solenoid is a 900W DC solenoid running on 110VDC.

There is a slight problem with a solenoid/relay back emf diode - as it clamps the spike it causes current to circulate round the diode/coil circuit, that current delays contact opening and draws a longer arc - the ragged contact surfaces weld easier!

For lower voltage method is to use a clamp zener in series with a regular diode to prevent forward conduction is better than blindly shunting the spike.

For a 110V solenoid you might be better off with a MOV spike suppressor.
 

strantor

Joined Oct 3, 2010
6,798
There is a slight problem with a solenoid/relay back emf diode - as it clamps the spike it causes current to circulate round the diode/coil circuit, that current delays contact opening and draws a longer arc - the ragged contact surfaces weld easier!

For lower voltage method is to use a clamp zener in series with a regular diode to prevent forward conduction is better than blindly shunting the spike.

For a 110V solenoid you might be better off with a MOV spike suppressor.
Again, I believe this incorrect. If adding a diode actually aggravates the arcing problem, then why is it such a common practice to add the diode? Why can I buy relays and solenoids that have the diode installed from the factory?

The reason coils cause arcing across the contacts because they are inductors, and inductors oppose changes in the flow of current. When you suddenly open the circuit, the inductor will keep the current flowing at whatever voltage is necessary (up to infinity, theoretically) until the field collapses. So with no diode, the voltage just spikes until whatever voltage is necessary to arc across and complete the circuit. When you install the diode, that current now has another option of where to go, and it does choose to take the path of the diode, not the open contacts. With the diode installed and the new current path option in place, the coil does not need to increase it's voltage to bridge any gaps and complete the circuit, so no spike occurs. Upon opening of the contacts (@T0), the voltage across the contacts should be 0V, and rapidly approach source voltage (120V). So if upon opening the contacts the voltage across them is 0, then why are you saying that this will make the arcing worse? Can you provide a published reference that supports your claims? Because I have not heard this before you & (to an extent) RB said it. The way I have just explained it is the way that I understand it, and if I am wrong I welcome the correction.
 

ian field

Joined Oct 27, 2012
6,536
Again, I believe this incorrect. If adding a diode actually aggravates the arcing problem, then why is it such a common practice to add the diode? Why can I buy relays and solenoids that have the diode installed from the factory?

The reason coils cause arcing across the contacts because they are inductors, and inductors oppose changes in the flow of current. When you suddenly open the circuit, the inductor will keep the current flowing at whatever voltage is necessary (up to infinity, theoretically) until the field collapses. So with no diode, the voltage just spikes until whatever voltage is necessary to arc across and complete the circuit. When you install the diode, that current now has another option of where to go, and it does choose to take the path of the diode, not the open contacts. With the diode installed and the new current path option in place, the coil does not need to increase it's voltage to bridge any gaps and complete the circuit, so no spike occurs. Upon opening of the contacts (@T0), the voltage across the contacts should be 0V, and rapidly approach source voltage (120V). So if upon opening the contacts the voltage across them is 0, then why are you saying that this will make the arcing worse? Can you provide a published reference that supports your claims? Because I have not heard this before you & (to an extent) RB said it. The way I have just explained it is the way that I understand it, and if I am wrong I welcome the correction.
I was referring to the relay contacts opening more slowly - this happens because the catch diode shunts the current back through the coil.

Maybe I just read more application notes than you do.
 

ian field

Joined Oct 27, 2012
6,536
Again, I believe this incorrect. If adding a diode actually aggravates the arcing problem, then why is it such a common practice to add the diode? Why can I buy relays and solenoids that have the diode installed from the factory?

The reason coils cause arcing across the contacts because they are inductors, and inductors oppose changes in the flow of current. When you suddenly open the circuit, the inductor will keep the current flowing at whatever voltage is necessary (up to infinity, theoretically) until the field collapses. So with no diode, the voltage just spikes until whatever voltage is necessary to arc across and complete the circuit. When you install the diode, that current now has another option of where to go, and it does choose to take the path of the diode, not the open contacts. With the diode installed and the new current path option in place, the coil does not need to increase it's voltage to bridge any gaps and complete the circuit, so no spike occurs. Upon opening of the contacts (@T0), the voltage across the contacts should be 0V, and rapidly approach source voltage (120V). So if upon opening the contacts the voltage across them is 0, then why are you saying that this will make the arcing worse? Can you provide a published reference that supports your claims? Because I have not heard this before you & (to an extent) RB said it. The way I have just explained it is the way that I understand it, and if I am wrong I welcome the correction.
***************************************************

http://educypedia.karadimov.info/library/13c3264.pdf
 

strantor

Joined Oct 3, 2010
6,798
I was referring to the relay contacts opening more slowly - this happens because the catch diode shunts the current back through the coil.

Maybe I just read more application notes than you do.
***************************************************

http://educypedia.karadimov.info/library/13c3264.pdf
Ah I see the confusion, you're talking about suppression on a relay coil, and everybody else is talking about suppression on a solenoid (which is what OP asked about).
 

THE_RB

Joined Feb 11, 2008
5,438
Au contraire. Don't understand why you say that. :confused: A reverse-biased diode across the coil will most definitely minimize the problem of the contacts being welded. The diode will carry the coil current when the contacts open, keeping the voltage transient voltage no higher than the forward voltage drop of the diode and essentially eliminating any contact arcing.
...

Whoops! You are correct, I missed in post #1 that he was using a relay to drive a relay, and thought there was only one relay with both coil and contacts being very separate! :eek: :)

Please ignore my previous post.
 