    What would cause a new transformer to get smoked?
    I bought a new transformer for my furnace that takes 120V down to 24V the Hertz matched that of the existing one, it worked great for about a week and then it tripped a breaker and literally smoked.
  2. GopherT
    Nov 23, 2012
    6,321
    4,047
    Short circuit somewhere.
  3. paulktreg
    Distinguished Member
    Jun 2, 2008
    625
    125
    VA rating the same?
    Roderick Young likes this.
  4. MaxHeadRoom
    Jul 18, 2013
    10,858
    2,525
    Improper/inadequate fusing/protection.
    Max.
  5. Sun Tek
    Apr 19, 2016
    11
    Yes they are the same.
  6. Sun Tek
    Apr 19, 2016
    11
    The transformer that I replaced was the original and had lasted approx. 5 years. I don't know what would have changed as far as fusing etc?
  7. Sun Tek
    Apr 19, 2016
    11
    I will check it out.
    Thx
  8. Sun Tek
    Apr 19, 2016
    11
    I was just thinking about it; if it were a short circuit, could it have worked for a week before it tripped?
  9. Alec_t
    Sep 17, 2013
    5,979
    1,138
    If you had to replace the original transformer, there must have been a fault that had developed with time. That fault would still have been present (unless you had since fixed it) when you put the new transformer in: hence the new transformer also failed. You need to locate the fault before replacing the replacement transformer ;).
    Sinus23 and #12 like this.
  10. #12
    Nov 30, 2010
    16,704
    7,354
    Transformers almost never commit suicide. You must find the cause before you smoke the next transformer.
    If you're a crafty type, you can add a fuse in the 24 volt wire to (maybe) save the transformer.
    The last one I did like this, I had 3 fuses hanging on the red wire until the electronic air filter popped its fuse. Then I knew who killed the transformer.
    GopherT likes this.
  11. GopherT
    Nov 23, 2012
    6,321
    4,047
    Post a picture of the board. We might be able to help you narrow down the issue.
  12. Sun Tek
    Apr 19, 2016
    11
  13. Sun Tek
    Apr 19, 2016
    11
    I will post a picture of the board.
    So you suspect something in the board and not in the 120V powering the transformer?
  14. MaxHeadRoom
    Jul 18, 2013
    10,858
    2,525
    Well you could blame the service Co. but highly unlikely!;)
    The fact it tripped a breaker indicates you do not have any or at least inadequate fusing.