Hey guys
I have been asked to determine the equivalent circuit for a single phase transformer connection with the following measurements.
Given the transformer rating = (125/50 V)(1095 – 115) 50Hz
Short Circuit Test Measurements - LOW VOLTAGE side
voltage = 5.6V
current = 2.1A
power = 9.9W
Open Circuit Test Measurements - HIGH VOLTAGE side
voltage = 238.6V
current = 37.5mA
power = 2.625W
Open Circuit Test Measurements - LOW VOLTAGE side
voltage = 99.3V
current = 0.3A
power = 8.9W
My attempt
For Short circuit
θ = cos^(-1)(P/V*I)
=32.665°
Z = V/I <32.665°
= 2.7<32.665° = 2.2729 + j1.4572
(referred to primary side)
Re = 2.2729
Xe = j1.4572
For Open circuit
θ = cos^(-1)(P/V*I)
=72.939°
Y = I/V <72.939°
= 157.166<72.939° = 4.612 x10 ^(-5) + j1.5024 x 10^(-4)
(Referred to the Secondary)
Rc = 1/4.612 x10 ^(-5)
= 21.6 kΩ
Xm = 1/1.5024 x 10^(-4)
= 6.65 kΩ
a = Vo/Vin
= 238.6/99.3
= 2.4
Rc (Ref to Primary) = a^(2)* Rc
=124.416 kΩ
... Seems a little high
Xm (Ref to Primary) = a^(2)* Xm
=38.304 kΩ
These values for Rc' and Xm' seem way out. Where did I go wrong
Also If I have a resistive load at the output. How would I go about calculating the Power at the load?
Would I Refer the load to the Primary??? using R' = a^(2)*R ?
Thanks guys .... I'm pretty confused.
voltage = 5.6V
current = 2.1A
power = 9.9W
voltage = 238.6V
current = 37.5mA
power = 2.625W
voltage = 99.3V
current = 0.3A
power = 8.9W
My attempt
For Short circuit
θ = cos^(-1)(P/V*I)
=32.665°
Z = V/I <32.665°
Re = 2.2729
Xe = j1.4572
For Open circuit
θ = cos^(-1)(P/V*I)
=72.939°
Y = I/V <72.939°
= 21.6 kΩ
= 6.65 kΩ
a = Vo/Vin
= 238.6/99.3
= 2.4
=124.416 kΩ
=38.304 kΩ