    I am using a relay with contact capacity 10A/277VAC and 15A/24VDC as a switch to control 10 fluorescent lamps. I found that the relay life span is decreased tremendously due to the contact welded. Is this due to inrush current and how do I protect the relay contact?
  2. beenthere
    Retired Moderator
    Apr 20, 2004
    15,815
    283
    If the relay contacts weld, the current must be well above the rating. What is the voltage and current requirement for each fluorescent fixture?
  3. chchuah
    Jun 19, 2009
    Thanks. The fluorescent is rated at 40W each. As I know, it is an inductive load and there are inrush current during start up. How to prevent the relay contact from welded in this case?
  4. beenthere
    Retired Moderator
    Apr 20, 2004
    15,815
    283
    You may need to use multiple relays to spread the inrush current across more contacts.