Reactive Power -Q-

Thread Starter

mo2015mo

Joined May 9, 2013
157
Hi guys,,
I wonder :eek: why we transmitted reactive power if the load just consumed the real power??
Can anyone explain that to me clearly??
 

Attachments

crutschow

Joined Mar 14, 2008
34,459
The reactive power is not intentional. It's a result of the various capacitances and inductances in the circuit. In the case of a transmitting antenna it can be a result of impedance mismatch between the RF amplifier, drive cable, and antenna impedance. If they are all matched then there is no reactive power.
 

Thread Starter

mo2015mo

Joined May 9, 2013
157
The reactive power is not intentional. It's a result of the various capacitances and inductances in the circuit. In the case of a transmitting antenna it can be a result of impedance mismatch between the RF amplifier, drive cable, and antenna impedance. If they are all matched then there is no reactive power.
Okay,, thanks thanks my friend for new information :)
 

WBahn

Joined Mar 31, 2012
30,071
As crutschow said, reactive power is unintentional. If we could figure out ways to do what we want without producing it, we would. But we usually can't, so instead we find ways to minimize it's detrimental impact. Often that involves generating opposing Q to cancel out the unavoidable Q, so you could say that this is a benefit of Q.
 

Thread Starter

mo2015mo

Joined May 9, 2013
157
As crutschow said, reactive power is unintentional. If we could figure out ways to do what we want without producing it, we would. But we usually can't, so instead we find ways to minimize it's detrimental impact. Often that involves generating opposing Q to cancel out the unavoidable Q, so you could say that this is a benefit of Q.
okay my friend,, I have understood what are you talking
BUT ,, i mean that
lets assume that ... there are system as attached photo
A generator has S1 = -1000+j268
A Motor has S2 = -1000-j268
and a transmission line(T.L.) between them has impedance is Z= 0+j5 Ω and the current through T.L. is 10.35 ampere
thus P = -1000 -(-1000) =0 W
Q = 268 -(-268) = 536 Var = I^2 * X

By power value ,P, and current direction through (in or out) machine , I can conclude the type of machine (Generator or Motor)
By Reactive power ,Q, value What can i conclude by this value ?? and what means this value Q= -268 or 268 or 536 Var ??
 

Attachments

Thread Starter

mo2015mo

Joined May 9, 2013
157
The sign of the reactive component tells you whether you are looking at net inductance or net capacitance.
okay,, thats mean Q for net inductive(absorbs) and -Q for net capacitive(supplied)
so i can said motor and T.L. is net inductive , generator is capacitive or What??
How generator is net capacitive ??
please explain more my friend with examples for that :) :) :)
 

Attachments

Last edited:

WBahn

Joined Mar 31, 2012
30,071
okay,, thats mean Q for net inductive(absorbs) and -Q for net capacitive(supplied)
so i can said motor and T.L. is net inductive , generator is capacitive or What??
How generator is net capacitive ??
please explain more my friend with examples for that :) :) :)
The source is generally considered ideal (though possibly with a source impedance associated with it to account for the major non-idealities) and so is neither inductive or capacitive. The phase angle between voltage and current in the source is dictated by the load. It's the load that is either inductive or capacitive.

If you assign the current so that it is going into the positive terminal of the device, then you are treating the device as a load and positive reactive power means the load is net inductive.
 

Thread Starter

mo2015mo

Joined May 9, 2013
157
The source is generally considered ideal (though possibly with a source impedance associated with it to account for the major non-idealities) and so is neither inductive or capacitive. The phase angle between voltage and current in the source is dictated by the load. It's the load that is either inductive or capacitive.

If you assign the current so that it is going into the positive terminal of the device, then you are treating the device as a load and positive reactive power means the load is net inductive.
okay ,, i.e. for previous attached photo the machine on the right side of sys is generator and -Q means capacitive load (leading P.F.).
and the machine on the left side is motor and +Q means inductive load(lagging P.F.) .
thanks very much my friend ,, I have 3 Q's as written below ...

-T.L. is inductive ??(and always all the time)

-If we need to correct P.F. ... firstly where we are used it?? In motor , by adding capacitive load to load??

-In industry,if we're correcting P.F. ==> reducing our electricity cost bill because reduces T.L. losses ?
 

bountyhunter

Joined Sep 7, 2009
2,512
Hi guys,,
I wonder :eek: why we transmitted reactive power if the load just consumed the real power??
Can anyone explain that to me clearly??
We don't "transmit" reactive power, it is a result of the load's characteristics. In fact, the power companies put giant capacitors on the pole to correct the power factor to offset the effect of the inductance in all of the appliances being fed power.
 

t_n_k

Joined Mar 6, 2009
5,455
okay my friend,, I have understood what are you talking
BUT ,, i mean that
lets assume that ... there are system as attached photo
A generator has S1 = -1000+j268
A Motor has S2 = -1000-j268
and a transmission line(T.L.) between them has impedance is Z= 0+j5 Ω and the current through T.L. is 10.35 ampere
thus P = -1000 -(-1000) =0 W
Q = 268 -(-268) = 536 Var = I^2 * X

By power value ,P, and current direction through (in or out) machine , I can conclude the type of machine (Generator or Motor)
By Reactive power ,Q, value What can i conclude by this value ?? and what means this value Q= -268 or 268 or 536 Var ??
Your example is somewhat confusing. if S1 & S2 both have a negative real power component then the related machines (generator & motor) must both be sending real power into the network. The motor would have to be in regenerating mode. I'm not sure where you get the zero net power result from.

I take your point that if a motor is taking real power from the network then clearly (excluding motor losses) the mechanical load driven by the motor demands that equivalent power to accomplish a particular task - such as pumping water. This power must come from one or more generators attached somewhere to the AC network.

The attendant Q values must simply reflect the fact that no physical motor has unity power factor and if it is operating at a certain output power then some of the current supplied to the motor must be flowing in equivalent reactive elements within the motor - such as (but not limited to) the reactive power required for energizing the motor's magnetic circuit.

Power factor correction is not limited to the placement of capacitors near the loads connection to a system. A consumer may opt to install PFC capacitors at their point of common coupling to reduce their reactive power draw from the power utility. Power utilities may charge consumers for reactive power draw.

Large scale power system operators may themselves take steps to regulate or control reactive power distribution within an AC network. See this link .... http://en.wikipedia.org/wiki/Synchronous_condenser
 

Thread Starter

mo2015mo

Joined May 9, 2013
157
Really thanks for you
bountyhunter t_n_k WBahn

my teacher answered me and said "we really needed to reactive power Q to establish the magnetic filed flux between the primary and the secondary coils "
 

WBahn

Joined Mar 31, 2012
30,071
Really thanks for you
bountyhunter t_n_k WBahn

my teacher answered me and said "we really needed to reactive power Q to establish the magnetic filed flux between the primary and the secondary coils "
While I would say that this is not a complete answer, it may well have been quite reasonable within the context of which it was being given.
 