Somehow I don't really understand your posts Max...........I'm not a native english speakerGee don't you read all the posts.
I just explained how that is implemented in the UK .
As a ground conductor think of the earth as a huge circular conductor.
Max.
Paulo............I believe I understand your problem. Please refer to the diagram in post #19. This will only work with that circuit, it will NOT work with a mains supply. Because the mains supply is reference to ground already.
Disconnect the ground. Get your meter out. A pretend meter will work, if you understand potentials and currents.
Start up your generator. To measure the voltage across the load, you will have to put the meter leads across the load. Red lead on top and black lead on bottom of load symbol. You will read an RMS of the supply ac voltage.
Now, remove the black meter lead, and connect it to ground. What voltage do you read on the meter? 0.
Put the black lead back on the bottom of the load. You will see the voltage again. Now take the red meter lead and connect it to ground. What voltage do you read? 0.
Now, take the red meter lead and put it back on top of load. You will see the supply voltage.
Now....while the generator is on...and you are reading the voltage across the load, connect a jumper from the bottom end of the load....to ground.
Did the meter reading change? No. Disconnect the ground from the bottom of load and put the ground at the top of load. Did the meter reading change? No.
Do you see what is happening here? It's a matter of reference. The ac generator has two output poles. Referencing one of these poles to ground does not effect power transmission.
The pole that we selected as ground, becomes a NEUTRAL conductor.
A neutral conductor is a conductor that USUALLY and NORMALLY has no potential or voltage on it. We took the potential off of it by grounding it.
But it still has the current potential. This can be most dangerous. Some idiot will measure a neutral and see no voltage on it..................and think it is safe to touch or to disconnect.
IF, or as soon as it is disconnected, the neutral will receive and establish the full "hot" voltage. This voltage is supplied thru the load.
That hot voltage will now be between the neutral and ground, You do not want to be between them.
All power generation is symmetrical (balanced) and gives us two equal potentials. (+ and - poles) By grounding one of the potentials, we can deliver the same amount of power with one potential. This gives us safety and a common reference of ground for the other potential.
The earth is a special conductor. It is a conductive surface like other conductors, but the earth conductor can actually source and sink electrons. It's an active conductor.
Notice I said electrons and not charge. That subtle difference will become important later in your studies, one way or another.
So, have you got the idea of a neutral ac leg now? And do you understand that current flows thru your neutral, but not thru the ground?
Being able to source and sink electrons at a local ground, is completely different than flowing electrons thru the ground from separate grounding points.
Electrons moving in and out of ground encounter little resistance. But the resistance thru the ground, to complete the power supply circuit, is variable for many, many reasons.
It has been tried and used in the past. That's why we use a neutral today.
The earth is a good source/sink, but in reference to itself, it is a poor conductor.
Earth is an electrical vertical device (in and out), not a horizontal one (across or thru).
At 1,000 kM away - you'll encounter a lot of resistance, so, no, you won't be able to use just one wire. But generally speaking, if you have two grounding rods - lets say just 10 meters apart and you have 1/2 of your source going to the load and the other end of the source grounded near by then you SHOULD be able to run a 10 meter wire long enough to test the voltage and should find very little loss. But it depends on how moist the ground is.
They say light travels 186,292 feet per second. But how much is one foot? How long is one second? If you were going to walk to the store and asked "How far is it" and I said it's 16 parsec's" I'll probably get an annoyed look from you. "What the llleh is a 'Parsec?'" you may ask. But if I said it's 3/10 of a mile, now you know. Based on a common frame of reference.
We call ground "Zero volts". But maybe it's really 1.21 gigawatts. Maybe it's trillions of trillions of volts. When you measure your 50 VAC generator you're getting 50 VAC because your point of reference is common ground.
As you can see from my picture, measuring between two common points - you're going to get zero volts (respectively). Suppose you have a battery, the positive terminal is connected to a light bulb. The bulb's other wire is connected to a copper pipe. Now, if you touch your meter probes both to the copper pipe - what voltage will you get? Zero? Yes. But suppose you reverse the connections of the battery and now the positive is connected to the copper pipe and the negative wire is directly wired to the light bulb; what would you get by touching your meter probes both to the copper pipe? Again, zero volts.
Your generator is grounded for safety reasons. If for some reason the case of your appliance (load or whatever) becomes shorted to the high potential. What happens if you touch the case and it's not grounded? You become the path of least resistance to ground. In other words, you get a shock if your source is grounded. That's why it's common to have a hot, neutral AND a ground in your homes electrical circuit. Should the case become hot - you don't die, the power is going somewhere, thus protecting you.
Now, if you use only a two wire cord like a lamp cord and your source is grounded, and you touch one of the wires - guess who's swearing and jerking hands away quickly. Ever leave skin on a screw because you touched something live? I have.
Ground is just that - ground. Whether it's zero volts or 1.21 GigaWatts - or whatever, it's still ground.
Not necessarily, you are using a conductive ball 12,000+ km in diameter, it is unknown.At 1,000 kM away - you'll encounter a lot of resistance, so, no, you won't be able to use just one wire.
The green voltage will be a little higher than the blue voltage. The longer the distance from the power supply, that the load is......the higher the green voltage will be, compared to the blue. The green voltage is equal to the load voltage + the voltage drop of the neutral conductor.
The purple voltage could vary a great deal. It will depend on the ground conditions between the generator and the ground connection 50,000 miles away. Not to mention the resistance of the meter lead.
Paulo, You say that you have studied for a few weeks now. You can not study electronics like other subjects.
You have to start at the beginning. If you don't study and learn the basics, you can not proceed.
All further understanding requires a knowledge of the fundamentals.
That means you have to learn dc circuits before ac circuits.
You are still confused. You need to study the relationship between potential, current and resistance first.
Whatever you do, don't play with ac circuits.
Good luck.
edit----corrected.