problem with CT connection
Discussion in 'General Electronics Chat' started by henyson, May 4, 2015.
  1. henyson
    May 4, 2015
    Hello!
    look at my attached image.
    This Connection gives wrong current on CT1 secondary winding. As soon as I disconnect CT2, CT1 gives correct magnitude of the secondary current.
    What am I missing here?
  2. Reloadron
    Jan 15, 2015
    1,044
    268
    CT2 is driving into a dead short as drawn, you are aware of that correct?
    Ron
  3. henyson
    May 4, 2015
    I have short-circuited the secondary of CT2 intentionally to minimise the burden.
    For example: 5 A -> 1A with CT1 and further 1A -> 1 A with CT2 which I measure with an ammeter.
    The problem is that the value on CT1 secondary is much lower than 1A ( if I have 5 running in the primary) as long as CT2 is connected
  4. Lestraveled
    May 19, 2014
    1,957
    1,217
    Due to inefficiencies in CT2, a dead short (0 ohms), is not reflected across the secondary of CT1. Remove CT2 and short the secondary of CT1.