Power for 3 Phase Y Conn. Load
Discussion in 'Homework Help' started by jegues, Sep 29, 2011.
  1. jegues
    Sep 13, 2010
    735
    43
    See figure attached for problem statement as well as my attempt.
    I'm having trouble finding the power dissapated across the transmission line.
    I thought this would be,
    P_{TL} = \sqrt{3}V_{L}I_{L}cos\phi, \quad \text{Where, } \quad cos\phi \quad \text{is the power factor across the transmission line}
    Where VL and IL are the line voltage and current across the transmission line.
    I_{L} = 150 \angle -36.87^{o}
    V_{L} = I_{L} \cdot Z_{TL}
    Where,
    Z_{TL} = (2.5 + j10.2) \Omega
    The solution gets the answer by doing the following,
    Re \left{ 3 I_{L}^{2} \cdot Z_{TL} \right}
    Can someone explain my confusion or clarify things?
  2. t_n_k
    Mar 6, 2009
    5,448
    783
    There are several ways of coming up with an answer but having determined the line current, I would have thought the simplest way of expressing the transmission line power loss would be
    P_{TL}=3|{I_L}|^2R_{line}
    or using your values
    P_{TL}=3*150^2*2.5=56.25kW
    Sorry that was per phase
    it should obviously read
    P_{TL}=3*150^2*2.5=168.75kW
    BTW. Your formula would work fine as well provided you convert the voltage drop across the line impedance to a line-to-line equivalent voltage drop.
  3. jegues
    Sep 13, 2010
    735
    43
    Where does your formula come from?
    I can see you did P = IV, where V = I/R, but wheres does the 3 infront come from?
    Will the math show how it comes about?
  4. t_n_k
    Mar 6, 2009
    5,448
    783
    No I didn't use P=IV - rather I used P=I^2R
    The RMS magnitude of the current in any line conductor is |I_line|.
    This current flows in the line resistance R_line of each of the 3-phase conductors.
    So the total power loss in the transmission line for all 3 conductors is
    3*|I_line|^2*R_line
    The phase angle of the current doesn't matter in this approach since current and voltage in the line resistances (as lumped elements) are always in phase.
  5. jegues
    Sep 13, 2010
    735
    43
    I mentioned after that V= I/R
    Hence, P=I^2R.
    Thank you for your other comments, this is much more clear now.
  6. t_n_k
    Mar 6, 2009
    5,448
    783
    I guess you meant V=I*R ....