Power factor correction
Discussion in 'Homework Help' started by Asad ahmed1, Jun 12, 2016.
  1. Asad ahmed1
    Feb 10, 2016
    68
    please help me through it ..
  2. DGElder
    Member
    Apr 3, 2016
    347
    87
    You make a mistake on the 3rd page. You assume that after adding the capacitor the apparent power does not change. The reason for adding the capacitor is to reduce the apparent power by shifting the pf closer to 1.0, i.e. reducing the current on the lines while still providing the same real power.
    Also reactive power is in VARs and apparent power is in VA.
    Asad ahmed1 likes this.
  3. Asad ahmed1
    Feb 10, 2016
    68
    If the Appearent power is changed so I would be getting S=(10+4.358) k?
    and after that (7-10)+(7.141j-4.31j)=p+jQc ???
  4. DGElder
    Member
    Apr 3, 2016
    347
    87
    I can't see the last line on page 2, but the rest looks OK to me. You have the correct values for the network before the addition of the capacitor.
    Page 3 is where you go astray.
    After adding the capacitor, in parallel, it draws reactive power only. The real power to the total network remains the same, but the reactive and apparent power will change. The original load still sees the same voltage so it will still draw the original S,Q and P. But, the added capacitor will draw reactive current.
    First determine the new total Q and the new S. You know the new pf and therefore the phase angle and you know P, so you can easily find Q and S.
  5. Asad ahmed1
    Feb 10, 2016
    68
    P after pf = 1
    p=s(1)
    p=10k
    and Q=4.358kVAR
    S=P+jQ
    S=(10+j4.358)K ???
  6. Asad ahmed1
    Feb 10, 2016
    68
    Qcj+p=V^2 ω C
    C=(Qcj + p/V^2 ω ) ???
    C=(2.831+3/(400)^2 2 π 60)
    C=96.5uF
  7. DGElder
    Member
    Apr 3, 2016
    347
    87
    I have to eat now, after dinner I will walk you through it. Not sure where you are going with pf=1, the new pf =0.9
    If pf=0.9 and P = 7KW, then what are Q and S?
  8. Asad ahmed1
    Feb 10, 2016
    68
    Iam sorry I was looking at another problem
    If Pf=0.9 the P=s(.9)
    p=10000*0.9=9000W (BUT The real power to the total network remains the same if P old = P new )
    arccos(.9)=-25.84
    And I get that you are saying that S is changed so 7k=s(.9)
    s=7777.7VA
    Q=S Sin(25.8)
    so S=(7+3.299)k
    S=S1-S2
    S=(7-7)+(7.141j-3.31j)k
    C=(3.831)k/(400)^2(2 π 60) C=63uF..?
    when
    power factor =.9
    if I do tan(25.84)=Q/p Q=3.389 almost same ?
  9. DGElder
    Member
    Apr 3, 2016
    347
    87
    C=(3.831)k/(400)^2(2 π 60) C=63uF..? this eq. needs parenthesis to be clear
    Almost correct
    What is the frequency?
    Define variables (s,S,S1,S2 ?) and don't skip intermediate steps, it's hard to follow, correct and is prone to mistakes. But I get the gist of what you did - looks good.
  10. Asad ahmed1
    Feb 10, 2016
    68
    frequency is 60Hz thanks for making my concept clear thanks alot....
  11. DGElder
    Member
    Apr 3, 2016
    347
    87
    "frequency is 60Hz thanks for making my concept clear thanks alot...."
    Your welcome - just hit the Like button.
    Your 1st .jpg states f as 50Hz
  12. MrAl
    Distinguished Member
    Jun 17, 2014
    2,562
    519
    But your first paper says that the frequency is 50Hz, so which is it, 50Hz or 60Hz ???
    Also, did you use 60Hz, because the paper says 50Hz ???
    Did you get 63uf for the cap, using 60Hz or 50Hz ???
    Obviously the frequency is very important, but the relationship between the frequency and the capacitor is linear:
    C=K/f
    with K a constant, so if the frequency is 60 to begin with and the capacitance is C1, then the required capacitance at 50Hz will be C2=C1*60/50.
    There is also a short cut formula for C we can look at later that does not require knowing the inductance nor parallel resistance, just the apparent power, the two power factors, the voltage, and of course the frequency of operation.
    I am posting the drawings again but more clear to read after enhancing the pictures, for the benefit of other readers.