    Hi there,

    I have a circuit consisting of four (single phase) induction motors. Each motor develops 15kW @ 80% efficiency. Operating at 0.75 lagging power factor. The total setup is supplied 240V @ 60 Hz.

    I need to work out how to correct the power factor to 0.8 lagging (total supply) using a shunt capacitor. I'm having a bit of trouble, but I've given it a go and I'd just like to check my answer.

    Power out = 15kW

    Total Power out = 15 * 4 = 60 kW

    Power in = 15/0.8 = 18.75kW

    Total input power = 18.75 *4 = 75kW

    Current drawn by each motor: 18.75kW/(200 * 0.8) = 117.2 A

    Supply current = 117.2 * 4 = 468.8 A


    Before Power Factor Correction:

    Motor power factor = 0.75 lagging

    Total Active Power = VI*0.75 = 240 * 468.8 * 0.75 = 84.4 kW

    Total Reactive Power = VI sin 41.4 = 240 * 468.8 * sin 414.4 = 74.4 kvar

    After Power Factor Improvement:

    Connection a cap doesn't change the P = 84.4 kW

    New power factor (lets call this phi') = 0.8 lagging

    Total reactive power = Ptanphi' = 84.4 *tan 36.86 = 63.2 var

    Cap reactive power Qc = 63.2 - 74400 = -74336.8 var

    Thus, Xc = V^2 / |QC| = 240^2 / 74.336.8 = 0.775 ohms

    C = (2*pi*f*Xc)^-1 = 1/(2 * pi * 60 * 0.775) = 0.0034 F = 3.4 mF

    So, for each motor, adding 3.4/4 = 0.85 mF of capacitance across the motor will correct the power factor to 0.8 lagging.

    Feedback is appreciated, thanks.
     
  2. t_n_k

    AAC Fanatic!

    Mar 6, 2009
    5,448
    782
    I have C(total) = 455.63uF

    Method used:

    Original System - uncompensated

    Total Power = 75 kW @ pf=0.75 lagging
    [phase angle = -acos(0.75) = -41.41°]

    Total Reactive Power = 75*tan(-41.4°) = -66.1438kVar

    Compensated System

    If the new pf is 0.8 then new phase angle = -acos(0.8) = -36.87°

    The resultant Total Reactive Power = 75*tan(-36.87°) = -56.25kVar

    Change in Reactive Power = +9.84kVar

    Compensating (Capacitive) Reactive Power required = 9.894 kVar = ωCV^2

    Therefor C =9.894 x 10^3/(2*pi*60*(240)^2)= 455.63uF
    (or 113.91uF per motor)

    Hopefully someone else will provide a third opinion which matches either of our answers.

    I think you may have gone astray in the motor current calculation ....

    If the total real power is 75 kW and the power factor is 0.75 then the apparent power is 100 kVA. Each motor then draws 25 kVA which equates to a motor current of 104.167 Amps at 240 V.
     
  3. Zaraphrax

    Thread Starter Active Member

    Mar 21, 2009
    47
    3
    I think you might be right actually (not enough coffee for me today obviously). That'd seem to make more sense than what I had. Let's see if someone else can confirm. :)

    Thanks for response.
     