Power Factor calculation

Discussion in 'Homework Help' started by Shahzad Rajpoot, Oct 16, 2014.

  1. Shahzad Rajpoot

    Thread Starter New Member

    Oct 16, 2014
    3
    0
    how can we determine leading or lagging power factor by wattmeter or by any other meter in lab?
    please help me
     
  2. studiot

    AAC Fanatic!

    Nov 9, 2007
    5,005
    513
    A traditional crossed coil wattmeter compensates for power factor, or may be calibrated in phase angle or power factor.

    In the lab alternatively we can use an impedance bridge sucha s a schering bridge to separately measure the resistive and reactive components.
     
  3. The Electrician

    AAC Fanatic!

    Oct 9, 2007
    2,282
    326
    Have a look at this:

    http://en.wikipedia.org/wiki/Power_factor

    You measure the load current and voltage separately, multiply the two values and that gives you apparent power S.

    Then measure the true power drawn by the load with a wattmeter; that gives you active power P.

    The power factor is given by PF = P/S
     
    Shahzad Rajpoot likes this.
  4. WBahn

    Moderator

    Mar 31, 2012
    17,757
    4,800
    Though this only gives you the magnitude of the power factor, and not whether it is leading or lagging.
     
  5. The Electrician

    AAC Fanatic!

    Oct 9, 2007
    2,282
    326
    Even though this is the Homework help forum, his question makes it sound like he's looking for lab help. I gave him one method to partially answer his question; the rest is up to him.

    I could have said "Get one of these:" http://www.laurels.com/phase.htm
     
  6. eprasadg

    New Member

    Jul 28, 2012
    10
    0
    Electricity department installs the meter where it reads KWH, KVarH and KVAH.
    Power factor =(KWH2-KWH1)/(KVAH2-KVAH1)
     
  7. Shahzad Rajpoot

    Thread Starter New Member

    Oct 16, 2014
    3
    0
    i m not asking the method to calculate power factor i wish to know the method to find leading or lagging pf
     
  8. WBahn

    Moderator

    Mar 31, 2012
    17,757
    4,800
    You can connect wattmeters to read VAR as well as watts. If you measure VARs, then whether it is positive or negative will tell you leading or lagging.
     
  9. The Electrician

    AAC Fanatic!

    Oct 9, 2007
    2,282
    326
    Connect a capacitor sized to draw a current of at least 30% (but not more than 95%) of your load current in parallel with the load. Measure the power factor with the capacitor in place as I described in post #3.

    If the PF improves (gets closer to 1), then your load PF (without the capacitor) is lagging. If the PF gets worse then your load PF is leading.

    Alternatively, use an oscilloscope to examine the phase relationship between load current and voltage.
     
  10. The Electrician

    AAC Fanatic!

    Oct 9, 2007
    2,282
    326
    How would one connect wattmeters to read VARs?
     
  11. WBahn

    Moderator

    Mar 31, 2012
    17,757
    4,800
    First, I am assuming something that is perhaps not a valid assumption, and that is that we are talking about three phase power here.

    The key is that there is nothing intrinsic about a wattmeter that makes it magically measure real power. It responds to the product of the voltage across one coil and the current through another coil -- in other words it is simply evaluating a mathematical relationship and displaying the result. Normally, you connect them so that the voltage coil is measuring the voltage across the load through which the current going through the current coil is going. But you don't have to do that, particularly in a multiphase system. By choosing which voltage and which current you apply to the wattmeter's coils, you perform the same math, but the relationship means something different.
     
  12. The Electrician

    AAC Fanatic!

    Oct 9, 2007
    2,282
    326
    Sounds to me like this is a lab exercise for the OP, so I would assume single phase. How would you connect wattmeters to measure VARs in a single phase system?
     
  13. The Electrician

    AAC Fanatic!

    Oct 9, 2007
    2,282
    326
    It's not this easy in a polyphase system if you want accurate results under all conditions. My Electrical Engineers Handbook says:

    "Any reactive power measuring device which depends on cross-connection of the voltage circuits will read incorrectly if both the voltages and the currents are unbalanced."

    This is likely the first lab where the OP is learning to make these sorts of measurements. Surely he wouldn't be learning on a polyphase system at first.
     
  14. WBahn

    Moderator

    Mar 31, 2012
    17,757
    4,800
    I have no idea what kind of lab the OP is taking -- it may well be a power lab since few other labs at most colleges ever deal with AC power circuits at all. Now, if he's taking a lab at a trade school then I don't know, but it would seem that there would be a good chance you are correct. I'm not sure what the handbook is referring to or whether it applies to what I am talking about -- I lack the context to determine that. Surely there are techniques that only work if the system is balanced.
     
  15. JoeJester

    AAC Fanatic!

    Apr 26, 2005
    3,373
    1,159
    Maybe the OP can post a link to his lab assignment.
     