Open-delta connection transformers

Discussion in 'Homework Help' started by nyasha, Feb 5, 2012.

  1. nyasha

    Thread Starter Active Member

    Mar 23, 2009
    90
    1
    So l have attached the question and my attempt to the solution. I think l answered all questions correctly....but for part c l do not know if l draw the phase angles of the winding currents and voltages with a 30 degrees phase shift between them ?
     
  2. t_n_k

    AAC Fanatic!

    Mar 6, 2009
    5,448
    782
    I would think the secondary windings are capable of carrying the full 543.5A at 460V line-line.

    So the total load power would be √3*460*543.5=433kW.

    Each transformer must carry half that power or 216.5kW.

    The primary kVA per transformer with rated winding current & voltage is still 250kVA so each transformer is running with a power factor of 216.5kVA/250kVA=0.866

    BUT ... the total 3-phase source power factor will be unity.
     
    Last edited: Feb 6, 2012
    nyasha likes this.
  3. nyasha

    Thread Starter Active Member

    Mar 23, 2009
    90
    1

    But wouldn't that damage the windings of the transformer ? Do we want that much current flowing into the windings of the transformer ?
     
  4. t_n_k

    AAC Fanatic!

    Mar 6, 2009
    5,448
    782
    No since that value is the rated current for the secondary winding of each of the 250kVA transformers. One can draw the rated current without any damage.
     
    nyasha likes this.
  5. nyasha

    Thread Starter Active Member

    Mar 23, 2009
    90
    1
    I am confused there. I thought the 250kVA was for three delta transformers connected. Which means when another phase is removed the power output decreases.
     
  6. t_n_k

    AAC Fanatic!

    Mar 6, 2009
    5,448
    782
    It's spelled out in the wording of the question which you might review ...

    So two single phase transformers, individually rated at 250kVA are connected in open delta.
     