Motor control logic

strantor

Joined Oct 3, 2010
6,798
I started plugging it into the simulator and realized right away a problem.
If M1 and M2 are the motor contactors, then there is nothing to retain them once the N.O.? start button is pushed and released?.
Max.
Yes, I pointed out to him in PM that he needs to latch past the start button with M1 & M2 N.O. contacts in parallel. He's fixed it already.
 

Thread Starter

Crimsonblood

Joined Nov 18, 2013
18
Yes, I apologize. I just forwarded the same message to everyone. M1, c3 on motor 1 and m2/c3 on motor 2 (aka the holding contacts) need to be extended to prior to the start button to work, credit to strantor.
 

MaxHeadRoom

Joined Jul 18, 2013
28,702
I checked it briefly with the simulator and it steps through the four conditions, except when it goes to repeat, both motor turn on off, I did not get much time tonight to dig deeper, hopefully tomorrow I will see if any thing pops up.
It could also be partly due to the faster acting PLC simulation, but if this bug is eliminated on the PLC then it may make it a bit more bullet proof.
Did you update your print?
When it cycled through correctly for one four step cycle , I did not see CR3 pick up at all!
Max.
 

strantor

Joined Oct 3, 2010
6,798
Looks good to me.

The only question I have is possible timing. On the first press if M is large and slow. Could cr pull in M2 before M/nc breaks?
I take that back. Cr is delayed by pull in time of M. ;)

The instruction were misunderstood by me.:(
I noticed the need to be able to stop motors between sequences. What I did not know is that it was required to do so.

That takes away strantors requirement for timing.

I don't think I've posted a spoiler. If I have let me know and I'll delete.
The timing issue I see is with cr3; as mentioned above, in a plc it will only be high for onc cycle, and it will work. With physical relays, the brief period during which it is on may not be enough time for m1 and m2 to close and latch, since they are bigger and slower. I don't know if this real world stuff matters for the exercises. OP, are you expected to build a work circuit and demonstrate?
 

MaxHeadRoom

Joined Jul 18, 2013
28,702
I made a couple of changes to seal CR3, worked like a charm on the simulator.
I did not see it originally as it was only on for one scan.
With discrete relays timing, this may, or may not be a problem.
Max.
 

Thread Starter

Crimsonblood

Joined Nov 18, 2013
18
The timing issue I see is with cr3; as mentioned above, in a plc it will only be high for onc cycle, and it will work. With physical relays, the brief period during which it is on may not be enough time for m1 and m2 to close and latch, since they are bigger and slower. I don't know if this real world stuff matters for the exercises. OP, are you expected to build a work circuit and demonstrate?
Yup, I gotta build it. It will be built tomorrow at 8AM, will post results and pictures.
 