Magnetic Contact instead of a relay?

Thread Starter

Kinoton

Joined Jan 20, 2014
34
Hi , I am converting a 3ph motor to run from a single phase inverter. All works fine but I would like to use remote switches to run the inverter instead of the buttons on the inverter itself. It makes sense to use the buttons on the machine (a cinema projector ) . Looking inside the machine there appears to be two magnetic contact switches in line with the 3ph to the motor. Using the inv I am currently by passing these switches but if I apply single ph to the terminal strip inside the machine and press the start button , one contact closes followed by the second. I think what is designed to happen is that the first one closes and sends 3ph through some resistors to provide a soft start , and then a timer cuts the 2nd mag contact in (and the 1st out) when the machine is at speed. My question is could I use one of these contacters to provide a run signal for the inverter. Obviously I will disconnect the original 3ph arrangement as this is no longer needed. Sorry so long winded!
 

MaxHeadRoom

Joined Jul 18, 2013
28,686
If by inverter you mean VFD you should not have any contactor between VFD and motor, one can be used on the input side for E-stop or power off.
If it is a VFD, all control should be done by the low level input terminals set up for this reason.
These do not need anything as large as a contactor but either normal P.B.'s or small control relays can be used.
Max.
 

MaxHeadRoom

Joined Jul 18, 2013
28,686
Normally the contactor is used only on the power input supply side for the reasons I mentioned.
It would not be used for the on/off low voltage control at all, this would be done with separate low voltage control, usually ~24vdc supplied by the VFD itself..
Max.
 

Thread Starter

Kinoton

Joined Jan 20, 2014
34
Thanks for that.
So if I wanted to use the buttons on the machine (start N/O) stop (N/C) I would need a relay to maintain the run signal ? I don't think the VFD I'm using has a built in 24vdc supply (omron sysdrive 3gvxv)
Cheers
 

MaxHeadRoom

Joined Jul 18, 2013
28,686
Page 2-14 of the manual, you just need contact closure P.B.'s the supply is internal.
Wire the buttons direct to the input terminals and the common.
There are two ways to do it, you can use one two position switch if need be, one way to run, the other stop.
Max.
 

Thread Starter

Kinoton

Joined Jan 20, 2014
34
Thanks Max. Yes , I've done something similar to that in the past using a locking PB but I wanted to make use of the ones that are already on the machine , which I believe are n/o momentary contact for the run button and n/c for the stop . If I wire these to the terminals then would it only run while I hold the run PB in ? Jon
 

MaxHeadRoom

Joined Jul 18, 2013
28,686
It is a little vague but it may be that by setting N02 and N36 you can set momentary input on start and stop setup.
It would be easy to test.
Max.
 

JWHassler

Joined Sep 25, 2013
306
It is a little vague but it may be that by setting N02 and N36 you can set momentary input on start and stop setup.
It would be easy to test.
Max.
'a little vague' is faint damnation! That's a data-sheet designed to piss-off an electrician.
The diagram for 3-wire control is on page 2-14.
 

MaxHeadRoom

Joined Jul 18, 2013
28,686
2-14 I believe Standard input is start & stop inputs momentary.
Also 10-2 n2=0?
And page 5-18 for multi-function setup, which you may not have to go into, try the combo's out and you should get the mom start stop i believe.
Max.
 