Inductors in parallel...

Thread Starter

Externet

Joined Nov 29, 2005
2,198
Hi.

Ten equal non-coupled inductances in parallel yield a total of one tenth of the inductance, is that right ?

The power factor correction needed in many factories increases with the number of motors in parallel they operate, is that right ?

Seems the more inductive motors in parallel, the less the inductance, but the need for power factor correction is not less with less inductance.

Where is the catch :confused:
 

thingmaker3

Joined May 16, 2005
5,083
As inductance decreases, current increases in direct proportion. Power is proportional to current, and therefore increases as well.
 

Thread Starter

Externet

Joined Nov 29, 2005
2,198
That explains it; ten motors at say 20 Amperes each is 200 Amperes to account, even for a tenth of inductance. The 200 figure raises the power factor

A single 20 Amperes motor, even having ten times the inductance does not raise the power factor by the same figure product, it is only ~a tenth of the above case.

Then, the amount of inductance in the load is not what makes the bulk of the power factor, the current is... if I got it.

Thanks thingmaker3 !
 