I need help replacing a heating Relay

Thread Starter

shocking

Joined Feb 9, 2013
3
I have a house built in the mid-70s in New York. One section of the house has electric baseboard heat. I have replaced the thermostat with a 24V digital. The relay is the original, so it is getting close to 40 years old and I would like to replace it before it fails, although it is functioning normally at the moment. I took a picture of the old relay and a picture of one that I purchased. Should I use the new relay or should I get a different one? Thanks for the help.
 

Attachments

thatoneguy

Joined Feb 19, 2009
6,359
If the wiring is the same, you can replace it, but the old one is rated for 220V/25A while the new one is only rated for 220V/22A They are close, but some headroom is always a good idea, so staying with 25A or larger would be my suggestion based on information given.

If you knew the total current draw by all heaters in the circuit, that would help a great deal.

Ideally, and electrician should do the installation, as you are controlling a great deal of power, fire is likely if something is done wrong. Home Insurance companies will often not pay if total loss was caused by owner modifications that weren't installed to code. The problem is knowing what "to code" is in your area. The North East is by far the most regulated area in the US when it comes to things like that.
 

#12

Joined Nov 30, 2010
18,224
Your new part looks like a time delay device. The old, "Klixon" heat relays used a heater to pop a bimetal that closes the contacts. You might not have what you expected.

Hook it up on the 24 volt side and see if it clicks on instantly or has several seconds (some take up to 90 seconds) of delay.
Edit: I looked it up and found a 75 second delay built in.

It might not be easy to get a 25 amp rated controller because of the ever increasing cheapitude of the manufacturers. 5KW will use 21.7 amps at 230V. That will work, but you can still buy 25 or 30 amp relays if you know what you're loking for.
 
Last edited:

Thread Starter

shocking

Joined Feb 9, 2013
3
thanks for all the help guys. I have no idea what the load is. All I can add is that there are 3 baseboards on the circuit, 2 X ten feet and 1 X 3 feet if that is any indication of what they would drawn. I think the breaker is a 20 amp.
 

thatoneguy

Joined Feb 19, 2009
6,359
Hook it up on the 24 volt side and see if it clicks on instantly or has several seconds (some take up to 90 seconds) of delay.
Edit: I looked it up and found a 75 second delay built in.
I'm not an HVAC expert, would the delay be a hinderance to a digital thermostat? I am unsure of the purpose of the delay, myself. Isolation by a thermal switch?

Info Page on Relay in OP

Honeywell R841C1227 is a 24 V Electric Heater Relay with SPST switching action (single pole, single throw).
The R841C1227 is used with two-wire, 24 Vac thermostat to control electric heating equipment such as baseboard, ceiling cable, duct heaters and can be mounted in any position. It also provides a versatile operation with each cycle of the thermostat(4 to 6 cycles per hour). The small size and silent operation of the R841 allow installation in a living area, utility room or basement.

Features:

  • Each relay switches up to a 5,000 W load;
  • Contacts make and break in about 75 second
 

#12

Joined Nov 30, 2010
18,224
In furnaces over 5000 watts, they are switched on in stages to minimize light dimming and start surge. In a furnace or heater up to 5000 watts, you don't need to stage the load.

The bother comes when the thermostat manufacturer decides to install a delay which then adds with the delay of the Honeywell "relay", and the brain board delay. In air conditioners, there is a necessary 3 minute re-start delay for the compressor which has to wait until the pressures equalize to start. Suddenly, you find the compressor has a delay, the controller in the air handler has a delay, and the thermostat has a delay, and you stand there for 10 minutes wondering if it's going to start or not because everybody wants to add a start delay, just because they can.

Normal relays isolate just as well as time delay relays.

Quick, install more microprocessors! We only have 3 redundant delays!
 
Last edited:

thatoneguy

Joined Feb 19, 2009
6,359
I don't understand why surge is an issue for baseboard heaters with one pole/circuit. I thought the isolation was thermal or similar, to provide a non inductive load to the thermostat.

Knowing that, I found this one, it has an extra 24VAC transformer to supply voltage, looks like the old one in the OP does as well on lower left. But it's only 10A. :( Honeywell RA89A1074

My search-fu is weak tonight. I can't find a Dual Pole Single Throw, 25A@240V rated relay with integrated 24VAC transformer.

I think that is what the diagram on the old one shows: DPST outputs (2 lines switched) 240V 25A contacts with integrated 24VAC transformer for powering the thermostat circuit if I'm reading it right.

--ETA: Ok, I found a rule of thumb as 250W/ft of baseboard heat. So the OP has a total of 3,250 Watts, or ~15A@220V. Using a DPST, the 10 foot section would need to 12 AFL contacts, and the 3ft would need smaller, 5AFL would be fine.

Found one.
Honeywell R841E1068 (Can be found cheaper elsewhere)

DataSheet for all Honeywell 841 series
R841E Models have two contacts, 24VAC transformer in enclosure.
 
Last edited:

#12

Joined Nov 30, 2010
18,224
Nobody said surge is an issue with baseboard heaters, only in furnaces over 5000 watts. That's because nichrome can be 1/2 or 1/3 its hot resistance when cold.

There are some old 120 VAC thermostats that can run a baseboard heater, and they don't even try for isolation. The 24 volt thermostats only control relays, a a few tenths of an amp each.
 

thatoneguy

Joined Feb 19, 2009
6,359
Nobody said surge is an issue with baseboard heaters, only in furnaces over 5000 watts. That's because nichrome can be 1/2 or 1/3 its hot resistance when cold.

There are some old 120 VAC thermostats that can run a baseboard heater, and they don't even try for isolation. The 24 volt thermostats only control relays, a a few tenths of an amp each.
I guess my question was, if there are 4 separate systems installed and all of them are delayed by 75 seconds, how is surge improved?
 

#12

Joined Nov 30, 2010
18,224
If all the delays are synchronized, it doesn't improve anything.
However, a bimetal and a heater is not a very accurate timer. Displacing the start events by as little as 2 or 3 seconds will accomplish avoiding side effects.
 
Last edited:

thatoneguy

Joined Feb 19, 2009
6,359
I get it now. There's a delay built into my furnace that doesn't start the blower until the fire has been started. In the summer, it doesn't start until the unit is cold.

I'm guessing that is based on time relays rather than actually waiting to see if it's "ready" with feedback?
 

#12

Joined Nov 30, 2010
18,224
A fuel burning furnace usually uses a "stack switch" that starts the fan when the plenum is hot enough to do you some good. Freon systems are predictable enough to use a time delay.
 