How to fix a Phase-Lead Compensator?

Discussion in 'Homework Help' started by woodmark75, Dec 16, 2014.

  1. woodmark75

    Thread Starter Member

    Dec 11, 2014
    36
    0
    I've just finnished trying to design a Phase-Lead compensator so that the step response fits the design requiements below:
    • Ts<4 secs (+/- 5% settling value output)
    • P.O.<16%
    • compensator has a zero at -1
    I used the 'angle criteion' method i.e. summing up the angles from the poles & zeros to a reference point & derived a compensator = (s+1.58)/(s+73.51). My root locus has been modified & the step output of the system now has P.O.<16%. But the Ts is still around 30 secs. How do I reduce this to within the spec?

    System specifications:
     
  2. t_n_k

    AAC Fanatic!

    Mar 6, 2009
    5,448
    782
    Frankly, you seem to be very confused. You have a clearly stated point that the compensator is specified as having a zero at -1 and yet your "design" comes up with a zero at -1.58. What are you doing?
     
  3. woodmark75

    Thread Starter Member

    Dec 11, 2014
    36
    0
    Edit: to first post the 1.58 should NOT be a zero. It is just the figure that the compensator pole must contribute. Used in the derivation of the actual pole s = -73.51. Sorry for the confusion....
     
  4. t_n_k

    AAC Fanatic!

    Mar 6, 2009
    5,448
    782
    So the the lead compensator isn't (s+1.58)/(s+73.51)? Or is it???
    If it is, what are the dominant roots you are seeking to fix on the root locus? What did you determine to be the value of K1 as the other requirement to satisfy this condition?
    Again, if this is the lead network design there are certain other considerations one should take into account.

    For instance, with the compensator function form

    \text{Gc=\frac{1}{\rho}\frac{(s+Zc)}{(s+Pc)}}

    the ratio

    \text{\rho=\frac{Z_c}{P_c}}

    is of importance.
    Generally it is considered good design to keep the ratio \text{\rho} to a value at least greater than 0.05 (with 0.1 being rather more desirable). Of course the ratio will by definition be less than unity for a Lead Compensator.

    Your very low value of

    \text{\rho=\frac{1.58}{73.51}=0.021}

    is inconsistent with good design practice.

    With respect to the placement of the compensator zero Zc, it would be worth your while to consider something nearer the process zero at -0.452 along with a modest ratio of the compensator zero to pole values - say with Zc/Pc=0.1

    It would also be worthwhile comparing the two cases where the lead compensator zero lies either to the left or right of the process pole at -1.25. The root locus form in either case is of significant interest.
     
    Last edited: Dec 18, 2014