how to calculate the backup
Discussion in 'General Electronics Chat' started by sumitk, Aug 1, 2012.
  1. sumitk
    Aug 1, 2012
    7
    how to calculete the backup of a online 2kva UPS connected with 6 batteries of 26ah each,if the load given is of 1kw ??
  2. crutschow
    Mar 14, 2008
    13,479
    3,367
    Not enough info. Need to know the efficiency of the UPS and the voltage of the batteries.
  3. sumitk
    Aug 1, 2012
    7
    voltage of each battery is 12V.
  4. t_n_k
    Mar 6, 2009
    5,448
    783
    Total kWh=V*(total Amp-hours)/1000
  5. sumitk
    Aug 1, 2012
    7
    according to your formula i m getting 56.16 minutes of backup,is it correct ??total ampere hour i have taken is 26ah * 6=156
  6. crutschow
    Mar 14, 2008
    13,479
    3,367
    Total kWh = (12 * 26 * 6) / 1000 = 1.8 kWh, thus you would get 1.8 hours of backup if the UPS was 100% efficient (which it is not) and you completely discharged the batteries (which you shouldn't do). Taking those factors into account I would estimate about 1 hour of backup.
  7. sumitk
    Aug 1, 2012
    7
    Thank you Zapper i agree with you
  8. sumitk
    Aug 1, 2012
    7
    but if the ups rating is 3kva insteed of 2kva ,with same number of batteries and same specification then what should be the backup.