Help me-3phase motor

Discussion in 'General Electronics Chat' started by mizwan88, Apr 21, 2015.

  1. mizwan88

    Thread Starter New Member

    Apr 21, 2015
    8
    0
    Machine breakdown
    1)Previously, the machine condition is ok but after our 3 phase induction motor problem we replaced it. the problem is the ammeter to show the value if motor start up is not going up. this machine use 2 induction motors 3 phase. only one motor will show the value at ammeter. I suspect the current transformer problem so I swap it then the value going up. But after I buy new current transformer and change it still have the same problem. the worst case 2 motors not showing any value ammeter when the motors turn ON.I already try to change other phase but it can on 1st try but after that still same problem. Can anyone help me?? Thank you.
     
  2. MaxHeadRoom

    Expert

    Jul 18, 2013
    10,542
    2,369
    Are the motors performing OK? just the ammeter not working?
    Do you have any details on the current transformer/meter etc?
    Max.
     
  3. mizwan88

    Thread Starter New Member

    Apr 21, 2015
    8
    0
    Yes,the motor performing ok only the ammeter.I am using MH current tranformer with ratio 60/5A,class 3 and burden 5VA. The ammeter also with same rating.
     
  4. MaxHeadRoom

    Expert

    Jul 18, 2013
    10,542
    2,369
    Do you have a blown or faulty meter maybe?
    A current transformer and meter is a pretty simple basic device, not alot to go wrong.!
    Max.
     
  5. mizwan88

    Thread Starter New Member

    Apr 21, 2015
    8
    0
    I think not,because yesterday already try it and it can work. For your information,this is new machine and still not send to our client. Previously,the motor problem because of 'humming'sound so we send to the manufacturer.
     
  6. MaxHeadRoom

    Expert

    Jul 18, 2013
    10,542
    2,369
    If new components then I would look at the correct selection or quality?
    Especially if motor appears to work correctly, can you confirm with clamp-on test meter?
    Max.
     
  7. mizwan88

    Thread Starter New Member

    Apr 21, 2015
    8
    0
    yeah also test it with clamp meter. the value shows 6.5 A.
     
  8. mizwan88

    Thread Starter New Member

    Apr 21, 2015
    8
    0
    you can refer attached picture
     
  9. MaxHeadRoom

    Expert

    Jul 18, 2013
    10,542
    2,369
  10. mizwan88

    Thread Starter New Member

    Apr 21, 2015
    8
    0
    can you explain how to make it?? and what are the effect after that??
     
  11. MaxHeadRoom

    Expert

    Jul 18, 2013
    10,542
    2,369
    You change the ratio of the CT by adding either primary turns of the motor conductor or the secondary.
    Wind a turn of the motor conductor as shown.
    Max.
     
  12. mizwan88

    Thread Starter New Member

    Apr 21, 2015
    8
    0
    Ok thank you Max.. I try it first..
     
  13. mizwan88

    Thread Starter New Member

    Apr 21, 2015
    8
    0
    Dear Max,

    I already solve the problem. Not because of CT but wrong selection of core size wire. Before this I use only 0.5mm but total length quite far so I change it to 2.5mm. so ammeter working fine right now. Anyway thank you for your help and info.
     