Would you re-post your solution.#6 Single P.B. toggle (flip-flop)?
Max.
.
The one where the two coils are kind of in series.
I can never find it when I need it.
Some of the ones google brings up don't work
Should be a sticky.
Would you re-post your solution.#6 Single P.B. toggle (flip-flop)?
Max.
.
I feel there should be a distinction made between "PLC ladder logic" and "Ladder logic." Although usually when someone says "ladder logic," they are referring to a PLC, but this is not always true, and Ladder logic was around before PLCs; just a style of drawing relay wiring. PLCs were modeled on the existing convention for describing control circuits, in a way that electricians could understand. You can draw almost any physical relay control circuit in ladder style, and most machinery OEMs that continue to use relay control for their machines, continue to use ladder diagrams. But there is no guarantee that if you drew and wired a physical relay ladder logic circuit and drew the and programmed the exact same thing in a PLC programming SW that the PLC would behave the same way as the physical circuit, due to the way a PLC processes the info (scan, write at end of cycle, etc.)The only thing is Ladder is based on Boolean arithmetic and you can do many things in R.L. that is impractical with physical relays.Just come across: "ladder logic". Maybe a useful source of ideas.
The basics are there though.
I should qualify that a little as early control systems were all relay logic before the advent of PLC's.
Max.
Sorry bout' that Max...The OP was questioning it, not me.
Post#5.
Max.
True, the originator of the PLC, Dick Morley designed it to replace the older mechanical relay logic of the time and to be able to display it in the same format as a hardwired schematic, especially for the shop floor maintenance crew.I feel there should be a distinction made between "PLC ladder logic" and "Ladder logic." Although usually when someone says "ladder logic," they are referring to a PLC, but this is not always true, and Ladder logic was around before PLCs;
.
This one? These are the relays and values I used.Would you re-post your solution.
The one where the two coils are kind of in series.
I spent a bit of time going over this and I don't see how it works. Can you explain it?This one? These are the relays and values I used.
Max.
Attached Files
File Type: pdf FlipFlop.pdf (164.9 KB, 9 views)
Short answer: yesMust be one I posted.
Does this work?
The following assumes the power supply voltage is twice the rating the coils and
not letting the smoke is dependent on not holding the button down
t0 no current flows
t1 pb1 is pressed but not yet released:
current flows through d2.1, PB1, d2.2, d1 coil - d1 is energized with twice the rated voltage
t2 pb1 is pressed but not yet released:
d1.1 closes, creating a ground loop through d2.1, pb1, d2.2, d1.1, d2 coil
d2 does not energize
d1 is still energized with twice the rated voltage
t3 pb1 is released:
ground loop eliminated, half power supply voltage is applied across d1 coil,
and half across d2 coil, through d1.1, assuming d1 stays energized (probable)
d2 energizes
t4 Both relays are energized and latched through d1.1, and will remain so
d2.1 and d2.2 have changed state
t...
t...+1 pb1 is pressed:
a loop is created from +V, d2.1, pb1, d2.2, d1.1, d1 coil
potential difference across d1 drops to 0
t...+2 pb1 is pressed but not yet released:
d1 deenergizes and d1.1 opens, double coil voltage rating is applied to d2
d2 remains energized
t...+3 pb1 is released:
all paths through d2 are cut
d2 deenergizes
d2.1 and d2.2 return to initial state
system is reset to t0
It just works.I spent a bit of time going over this and I don't see how it works. Can you explain it?
It is something you should not do now in hard wired systems.Something you can't do in PLC ladder is a standard motor starter. It has the overload relay in the common side.
I may play with some bosch relays later. They're pretty voltage tolerant.Short answer: yes
[/CODE]
I suspect that most relays would hold in down to half voltage, but circuit demands d2 to energize on half voltage, assuming your supply matches the coil ratings. This is why I assumed supply should be double the coil ratings.I may play with some bosch relays later. They're pretty voltage tolerant.
It may be that the switch from full 12v on one to series connection gives a little boost. I believe they hold in down to a few volts.
Would be nice if 12v relays would work on a 10 v system. Have my doubts also.
I agree but I am still seeing brand new motor starter packages coming with OLs on low side .It is something you should not do now in hard wired systems.
It was commonly done at one time but now is frowned on and may even be in the current NEC or NFPA79.
But there was a concern that if the coil on the grounded neutral side or wiring to the O/L's were to develop a ground, it would render the O/L's inactive.
So the current thinking is to place them in the supply side to the coil for this safety reason.
Max.
I did a little research a while ago to find out how this came about, the only explanation I found that evidently it was claimed to make the wiring easier in a remote starter units for some reason, but I know for sure it got carried over to large enclosure control systems for a reason I could never fathom?I agree but I am still seeing brand new motor starter packages coming with OLs on low side .
I believe the rationale is this: if the OL contacts were on the high side, and a short to ground were to occur (likely) between the OL contacts and the coil (unlikely, but possible I guess), it could weld the OL contacts closed. Then you have no OL and you don't know it. But by putting them on the low side, there is no chance of them being welded, thus ensuring that the overload will always be able to do its job (ok, not always, but usually)I did a little research a while ago to find out how this came about, the only explanation I found that evidently it was claimed to make the wiring easier in a remote starter units for some reason, but I know for sure it got carried over to large enclosure control systems for a reason I could never fathom?
Max.