    I have been given this in my revew question
    A diesel plant uses 100mL of Fuel in 25 seconds, when driving a 10 pole, 3 phase generator delivering a load at 50Hz, 415v ,100A, 0.8pf lagging. Assume the generator efficiency is 0.85 and the fuel energy is 42.5MJ/L. (3.6MJ = 1kWh)
    Calculate the following
    Generator output
    Power = 1.73\times Volts \times I \times Pf
    1.73\times 415 \times 100 \times 0.85=61.02kW
    so for 1 hour = 61.02kWh
    Engine output
    Syn speed of generator = (120\times f)\div P
    (120\times50)\div 10 = 600rpm \rightarrow 360000rphr
    and the engine uses  100mL = 25sec
    Therefore
    400mL = 1min \rightarrow 24L = 1 Hr
    So if I use the 42.5MJ/L and multiply but 24 L i get 1020MJ/L
    1020 \div 3.6 = 283.33 kwh
    Overall efficiency when supplying the load.
    61.02 \div 283.33 \times 100 = 21.5%
    Have I managed to do this correctly ?...
  2. t_n_k
    Mar 6, 2009
    5,448
    783
    Firstly you've put the wrong value for the load pf - given as 0.8 while you've used 0.85 which is the quoted gen efficiency.
    You've also gone about solving this in a rather convoluted manner.
    Take the fuel for instance -
    Consumption is 100 mL in 25 sec or 4 mL per second.
    This equates to (4/1000)*42.5E6 Watts [Joules/sec] = 170kW
    Which is the maximum achievable power (at 100% efficiency) from the fuel at the indicated rate of consumption.
    This is required to operate a load of
    P_{load}=\sqrt{3}*V*I*(pf)=\sqrt{3}*415*100*0.8=57.5kW
    I would think the overall efficiency would then just be
    \eta=\frac{P_{load}}{P_{fuel}}*100%
    You would not include the generator efficiency in the overall efficiency calculation. You would however need this to find the engine output power - which you could do by working back from the generator output power.