Effects of leading power factor

Discussion in 'General Electronics Chat' started by kram.nacnud, Jul 18, 2008.

  1. kram.nacnud

    kram.nacnud Thread Starter New Member

    Joined:
    Jul 18, 2008
    Messages:
    1
    In a 3 phase system the municipality will measure & bill on the kVA reading, irrespective of the power factor.

    In a typical system the power factor is lagging and as such the customer must install power factor correction to reduce cost.

    What happens in a case where the power factor is leading? Will the power meter be able to compensate for this and in effect reduce the cost?
  2. mik3

    mik3 Senior Member

    Joined:
    Feb 4, 2008
    Messages:
    4,846
    Location:
    Cyprus, but now in UK (GMT+0)
    No, it wont reduce the cost. You have to install a power factor correction device for leading power factor if your current power factor correction device is not able to do that.
  3. thingmaker3

    thingmaker3 Retired Moderator

    Joined:
    May 16, 2005
    Messages:
    5,072
    Location:
    Rural, Oregon GMT -8
    Actually, many power companies will charge more if the power factor is below a standard minimum value.
  4. foolios

    foolios Active Member

    Joined:
    Feb 4, 2009
    Messages:
    135
    Location:
    U.S.
    Can you explain why this is so?
    I've heard of how power companies are thinking about charging residential customers for reactive loads because the times have changed.
    What does this all mean?
    How does a poor power factor cause there to be more cost? I've heard something about heating up the lines because of inductance, but how does this all play into costing the user more money?
  5. KL7AJ

    KL7AJ E-book Developer

    Joined:
    Nov 4, 2008
    Messages:
    1,604
    Location:
    North Pole, Alaska
    For large industrial customers, a highly reactive load can cause extra stress on transmission components, especially substations. It's not the lone customer, but the cumulative efffect of a lot of low-power-factor customers that make things hard on equipment...even though the actual power consumptions is less. In generaly, most transmission facilities are optimized for maximum efficiency at around 90% power factor.

    Eric
Similar Threads
Forum Title Date
General Electronics Chat What are the effects of hot/neutral reversed wiring? Sep 1, 2013
General Electronics Chat What adverse effects of the toroidal transformer do to the mcu Mar 24, 2013
General Electronics Chat loading effects Dec 10, 2012
General Electronics Chat Help in MGS gun led effects Jun 22, 2012
General Electronics Chat 555 Timer Control Voltage pin and it's effects on cap charge Aug 15, 2011

Share This Page