earthing

Discussion in 'Homework Help' started by Geney, Jul 12, 2012.

  1. Geney

    Thread Starter New Member

    Apr 2, 2012
    18
    0
    what happens if the earth wire coming from a building comes in contact with an underground metal pipeline.:confused:
     
  2. MrChips

    Moderator

    Oct 2, 2009
    12,449
    3,365
    Nothing. The metal pipe is also earth ground.
     
    Geney likes this.
  3. Geney

    Thread Starter New Member

    Apr 2, 2012
    18
    0
    oh what if the earth wire of the next building also touches the metal pipe line??? is there any flow of current to the next building??
     
  4. #12

    Expert

    Nov 30, 2010
    16,343
    6,828
    Zero volts plus zero volts plus zero volts is still zero volts, all day and all night, across as many buildings as you want.
     
  5. n1ist

    Active Member

    Mar 8, 2009
    171
    16
    Actually, you can have a current flow on a common pipe in certain fault conditions. For example, look at the case where two houses are fed from the same transformer and share a common conductive water pipe. If the neutral wire on the service drop is broken (on the street side the main bonding jumper between neutral and ground) on one of the houses, neutral current will flow through the common water pipe and back out the other house's neutral.

    /mike
     
  6. mcgyvr

    AAC Fanatic!

    Oct 15, 2009
    4,771
    971
    Google "earth potential rise" to find out why that's not always right
     
  7. #12

    Expert

    Nov 30, 2010
    16,343
    6,828
    Is this the section where we answer homework questions or the NIST?
    The OP did not specify a damaged ground, a fault conditon, or a high amperage that would cause an "earth potential rise".
    He/she asked about the "earth wire" which is supposed to be connected to a buried pipe in the first place, and not carry any noticable current unless there is a fault condition.

    Geez, where do you guys get this stuff?
     
    Last edited: Jul 17, 2012
  8. aprillove1719

    New Member

    Jul 17, 2012
    13
    0
    i research something on how a 230V a.c. supply is derived from a 3-phase 415V transformer, noting also that a consumer's neutral wire connects to the transformer's star/ neutral point further away. A separate "protective" earth (the steel armour of the underground cable) runs between the consumer's earth terminal and the (earthed) star point of the transformer as well.

    So:
    It's widely understood that the need for "earthing" is a safety measure designed to prevent electric shock from wiring faults or insulation breakdowns.
     
  9. Wendy

    Moderator

    Mar 24, 2008
    20,766
    2,536
    I do not want to distract from the OPs question, so I won't. The real world is much more complex. If anyone wants to start a separate thread to discuss the exceptions start it and then PM me.

    In an ideal world all grounds are the same. In the real world they aren't.
     
  10. #12

    Expert

    Nov 30, 2010
    16,343
    6,828
    @n1ist

    That exact thing happened at my house about a week or two ago. (I posted the problem and the cure on this site.) If the OP on this thread says anything to indicate a fault condition, I am ready to answer in minute detail.
     