    I would like to know why you have 2 short the secondary terminals of a curent transformer before disconecting them
     
  2. retched

    AAC Fanatic!

    Dec 5, 2009
    5,201
    312
    What? You dont.

    Are you thinking of a capacitor?

    Or do you have an enemy who wants you dead that told you that?
     
  3. Wendy

    Moderator

    Mar 24, 2008
    20,766
    2,536
    This needs to be in the electronic chat area.

    Welcome to AAC!
     
  4. t_n_k

    AAC Fanatic!

    Mar 6, 2009
    5,448
    782
    It is recommended that a CT not be operated with an open circuit secondary - if that's what you mean.

    The problem is that there is the risk of getting a very high secondary output voltage in the open circuit secondary condition - which may be hazardous to personnel.

    If a CT is in circuit (primary current flowing) but not connected to anything on the secondary side, then the recommended practice is shorting the secondary.
     