I would like to know why you have 2 short the secondary terminals of a curent transformer before disconecting them
 

Wendy

Joined Mar 24, 2008
23,429
Feedback and Suggestions Forum for providing feedback and suggestions about All About Circuits, including corrections to the e-book. This forum is not for getting help with technical questions.
This needs to be in the electronic chat area.

Welcome to AAC!
 

t_n_k

Joined Mar 6, 2009
5,455
I would like to know why you have 2 short the secondary terminals of a curent transformer before disconecting them
It is recommended that a CT not be operated with an open circuit secondary - if that's what you mean.

The problem is that there is the risk of getting a very high secondary output voltage in the open circuit secondary condition - which may be hazardous to personnel.

If a CT is in circuit (primary current flowing) but not connected to anything on the secondary side, then the recommended practice is shorting the secondary.
 