current drawn by motor

Thread Starter

shahnawaz

Joined Dec 30, 2008
37
Hi all,

i am trying to make an Auto Transfer switching(ATS) pannel for 03 input supply with one output supply.
my load is 8 x 10HP 3/p motors. please tell me how much current an AC 10HP 3/Phase motor can drawn. my friend said its as per below farmula
to convert the HP into Watt -10 x 746
to get the amp frm the watt -7460/400
total current taken by the motor -18.65amp

so please tell me is it the right farmula. if not then how i can calculate to get the exact ampere of a 10hp 3/p motor.

thanks in advance
 

BillB3857

Joined Feb 28, 2009
2,571
That formula does not consider starting current which can be as high as 3X running current.
The best way to know the motor current requirement is to read the nameplate on the motor.
 

Dodgydave

Joined Jun 22, 2012
11,307
3phase motor formula



HP x 746 =Amps
1.73 x E x Eff x PF


rule of thumb says 1.25Amps per HP


E= Voltage
Eff= Efficiency
PF= power factor correction
HP= Horse Power
 

GetDeviceInfo

Joined Jun 7, 2009
2,196
not sure what your local codes are, but in North America, the code states that nameplate data is your first source. Calculations are allowed, but if you don't know amps, how would you know pf/efficiencies?
 