current draw
bwd111
Joined Jul 24, 2013
117
25kW operating across a balanced three-phase 460v what is the current draw?
I came up with 54.35A
bwd111
Joined Jul 24, 2013
117
Those two answers only differ by 0.2%. What more can you expect, especially when odinhg indicated that the answer was approximately 31.34A.
Why wont this formula work P = I*V, so 25,000W = I * 460v? The answer comes up to 54.35A
WBahn
Joined Mar 31, 2012
30,088
Because that formula applies to a device in which you have two terminals across which V appears and the I going in one terminal and out the other. It also assumes that the V and the I are in phase.
With a three-phase netwrok, you have three terminals. Across any two of them you have V (but the pairs have phase shifts of 0, +120°, and -120°). This means that you have three supplies dumping power into it. But the reason why the total power isn't 3VI is because the voltage and the current aren't in phase on any pair of legs.
Work through the analysis on either a delta or a wye connected load and you should see how it works out. In particular, focus on the relationship between the line-to-line voltages compared to the line-to-neutral voltages.
t_n_k
Joined Mar 6, 2009
5,455
Keep in mind the 25kW is perhaps distributed over 3 phases.
If the line-to-line voltage is 460 volts then the line current would be
I_line=25000/(Vll*√3)=31.38 Amps.
donpetru
Joined Nov 14, 2008
185
Current draw depends on the power factor, power load and voltage.
Mathematical relations for the calculation are:
Option 1: - use voltage between phases:
I = P / (1.73 * V_line * cos_Fi)
where: I - current draw, P = 25kW, V_line - voltage between phases; cos_Fi - power factor (<=1).
Option 2: - use voltage between phase and neutral:
I = P / (3 * V_phase * cos_Fi)
where: I - current draw, P = 25kW, V_phase - voltage between phase and neutral (V_phase = V_line / 1.73); cos_Fi - power factor (<=1).
If you apply any of the two above mathematical relationships, the result is the same.
You should take into account a power factor of 0.5, to cover all cases.
donpetru
Joined Nov 14, 2008
185
My statement above, about power factor of 0.5, was made in the event that it is not known type of load.
LATER EDIT: If the load is resistive then the power factor is equal to 1.
bwd111
Joined Jul 24, 2013
117
this was the formula we were shown and is different that what you all have shown me. kw*100/1.73*e*PF
WBahn
Joined Mar 31, 2012
30,088
Perhaps you should consider changing schools and going to one that is actually going to teach you correct information.
bwd111
Joined Jul 24, 2013
117
The answer came out the same so both equations worked. Schools not the answer its who you know. Thanks again for your help and I learned soething as well
WBahn
Joined Mar 31, 2012
30,088
Didn't one giver you 54A and the other 31A?
I don't follow. If you believe this, then why are you in school at all? Or do you figure that all you need to do is get a piece of paper and then rely on getting someone to do a favor for you and give you a job?
Your welcome, and I hope so.