    Hi everyone!
    I want to use a contactor to on/off a pump. in this case I have a daily timer which has a 16A relay in the output.. so anybody knows the diagram circuit ??
    thank you
    Eric :)
  2. BillB3857
    Feb 28, 2009
    2,402
    348
    Single phase or 3 phase? Input voltage for timer? How much current does motor draw? Coil voltage on contactor?
    eric_s88 likes this.
  3. MaxHeadRoom
    Jul 18, 2013
    10,830
    2,500
    Here's a few combinations!
    Max.
  4. eric_s88
    Apr 20, 2011
    157
    single phase ! 220V for timer , I dont know about motor current draw and coil voltage :(
  5. MaxHeadRoom
    Jul 18, 2013
    10,830
    2,500
    16amp for the timer contact is ample for picking up a contactor, if you do not have it now, you have to decide what coil voltage and AC or DC.
    Then as previously mentioned, you need to select the contactor for current or HP rating.
    If you obtain a 3ph version that will cover for both 1ph and 3ph.
    Also do you need a manual override or stop?
    All things to consider.
    Max.
  6. BillB3857
    Feb 28, 2009
    2,402
    348
    If the motor is single phase and low enough current, do you really need a contactror?
  7. #12
    Nov 30, 2010
    16,663
    7,310
    As a crude estimate, 16 amps of 220V will easily run 2 or 3 horsepower worth of pump. What BillB said, You might not need a contactor.
    something like this?
  8. eric_s88
    Apr 20, 2011
    157
    thank you all.. I think the pump has a 1HP motor. and as #12 said, a 16A timer would run this motor easily. but what about start of the motor ?? I think it would draw much more of current at the startup.. would't it ??
  9. #12
    Nov 30, 2010
    16,663
    7,310
    Yeahbut...contacts are rated for start surges.
    If that was not true, I'd need an 80 amp contactor for my 2 HP air conditioner.
  10. eric_s88
    Apr 20, 2011
    157
    thats a good news. thank you Mr #12 ;-)
  11. MaxHeadRoom
    Jul 18, 2013
    10,830
    2,500
    Timer and relay contacts are rated by AC resistive, inductive and DC load.
    So the 16a most likely is the AC resistive load.
    If the timer is an expensive unit, you might consider using an intermediate device to carry the current to avoid failure of the more expensive unit.
    Max.
  12. eric_s88
    Apr 20, 2011
    157
    thank you... :) if the timer relay contacts are able to carry the surge current of motor start, thats affortable to use the timer... I think, right ?
  13. MaxHeadRoom
    Jul 18, 2013
    10,830
    2,500
    That's the chance you take.
    As I said, it depends on the value of the timing device and/or if you want to take the gamble. ;)
    Max.
  14. eric_s88
    Apr 20, 2011
    157
    I've found out sth not good! in the timer datasheet I read that the 16A output current could be used for resistive loads. and only 3A for incudtive loads.. so I have to use contactor for driving a 1HP motor.. and I think.. I'm right friends ?
  15. #12
    Nov 30, 2010
    16,663
    7,310
    Couldn't hurt, and cheaper to fix when it wears out.