Connect Efector Kapazitiz to PLC

Discussion in 'Homework Help' started by Ch3st, Apr 9, 2015.

  1. Ch3st

    Thread Starter New Member

    Apr 9, 2015
    2
    0
    Model: KI-3015-BPKG/KI5062

    How would I connect this sensor to a PLC?
     
  2. MaxHeadRoom

    Expert

    Jul 18, 2013
    10,507
    2,368
    That sensor has a PNP output, so it sources the load to -ve.
    The BN is +ve supply the BK is the load or input to the PLC, the BU is the common, if using a solid state PLC input, it depends if the inputs are sink or source.
    If opposite to the sensor, you may have to invert the output.
    Max.
     
    Ch3st likes this.
  3. Ch3st

    Thread Starter New Member

    Apr 9, 2015
    2
    0
    Thank You so much! We're doing a class project and making a working conveyor that'll use this sensor at the start and end. I'll have one more question of another sensor on this upcoming Tuesday. Yet, what you have told me that this other sensor has a logo on it as well that have this symbols on it.
     