Would it be safe to replace a devices 15 amp circuit breaker with a 12 amp breaker with the same voltage ratings? Also going the other way could a 20 amp breaker with proper voltage ratings be used in a circuit rated for 15 amps safely?
 

alfacliff

Joined Dec 13, 2013
2,458
the 12 volt replacement would be safe, but would trip more often. the 20 should not be put in since it would trip 5 amps later than the 15.
 

DC_Kid

Joined Feb 25, 2008
1,072
you can downsize, you cant upsize unless the wire connected to the OCD can support the up-sizing, etc. and, also depends on what the OCD is protecting, thus up-sizing, even if the wire can support it, may cause components to die, etc.
 

wayneh

Joined Sep 9, 2010
17,498
As noted, you cannot safely upsize the breaker without a lot of research. You would need to have full knowledge of every protected device on the circuit - every wire, switch, outlet and so on. Where is the weakest link? The SAFE design makes the breaker the weakest link.

A qualified electrician that is familiar with local codes and how they have changed, and how your home is likely wired, MIGHT be able to comment on whether going to a larger breaker is possible. Running another circuit is usually the batter option, if you need more juice somewhere.
 