Battery cables

Discussion in 'General Electronics Chat' started by superway, Jul 1, 2011.

  1. superway

    Thread Starter Active Member

    Oct 19, 2009
    128
    0
    Hello,

    My battery bank required 0/4 size of cable, but I don't have that big cables, but I do have 0/1 size. So instead of 0/4 size wire, can I use double 0/1 size to connect to battery bank?

    Thanks for help

    ken
     
  2. kubeek

    AAC Fanatic!

    Sep 20, 2005
    4,670
    804
    Yes, two awg 0 should have the same cross section as one awg 0000.
     
  3. mcgyvr

    AAC Fanatic!

    Oct 15, 2009
    4,771
    971
    There are certain standards that might not allow paralleling of cables or require certain requirements that must be met.

    Being cheap is never a good thing when running power cables....
     
  4. superway

    Thread Starter Active Member

    Oct 19, 2009
    128
    0
    During loading about 350Adc to battery bank, is the double 0/1 awg cable able to handle the load?

    Thanks
     
  5. SgtWookie

    Expert

    Jul 17, 2007
    22,182
    1,728
  6. mcgyvr

    AAC Fanatic!

    Oct 15, 2009
    4,771
    971
    According to the national electrical code
    0 AWG (commonly referred to as 1/0) will carry 150 Amps if enclosed/buried,etc... (w/75deg C terminations)
    or 230 Amps in free air (w/75 deg C terminations)

    If this application is in the US you better follow the NEC and the installation manual for any products you are using.. If not you could be held liable in the event of a fire,etc...
     
  7. Jaguarjoe

    Active Member

    Apr 7, 2010
    770
    90
    Doesn't the required voltage drop/cable length/resistance have something to do with this?
     
  8. #12

    Expert

    Nov 30, 2010
    16,355
    6,852
    Yes. The resistance of the cables determines the heating that will happen. The insulation is carefully measured and rated so it will not degrade when used according to the tables that wookie referenced.
     
  9. nsaspook

    AAC Fanatic!

    Aug 27, 2009
    2,913
    2,187
    If you do use two or more cables be sure to fuse each separately for fire protection if one cable opens.
     
  10. Kermit2

    AAC Fanatic!

    Feb 5, 2010
    3,795
    951
  11. Jaguarjoe

    Active Member

    Apr 7, 2010
    770
    90
    The degradation of the insulation depends upon the type of insulation. That's not charted here.
     