Average of three analog signals
Discussion in 'The Projects Forum' started by amitaashu, Aug 12, 2013.
  1. amitaashu
    Aug 12, 2013
    HI
    We are measuring three analog signals ( temperature) at a single duct and want to calculate the average value of the ( i.e. [1+2+3]/3 ) so I am looking for an electronic circuit through which I can calculate the average of them and generate single analog output.
    The input / output details are
    Input1,2,3: 4...20mA
    Output1: Avg( Input1,2,3 )
  2. Shagas
    May 13, 2013
    802
    74
    What are you using to measure the temperatures?
    amitaashu likes this.
  3. kubeek
    Sep 20, 2005
    4,687
    805
    First you would convert the 4-20mA signals into 0-x mV signal, sum the three signals using an opamp, divide by three using voltage divider, then convert the result back into 4-20mA.
  4. amitaashu
    Aug 12, 2013
    Dear Shagas
    We are using 2-wire transmitters. They are converting mV signals from thermocouple to 4..20 mA signal.
  5. amitaashu
    Aug 12, 2013
    Dear Kubeek
    can u suggest any type of converter or instrument available in market to fullfill the required pupose.
  6. MrChips
    Oct 2, 2009
    12,624
    3,451
    Kubeek already said it. You have to convert 4-20mA to voltage.
    Then sum the voltage using a summing amplifier (simple op-amp configuration).
    Then convert voltage back to 4-20mA if you are not able to work with the voltage.
  7. Shagas
    May 13, 2013
    802
    74
    I'm interested as in how one would convert a few mA into a reasonable voltage.
    Using 0.01ohm current sensing resistors ? or Using a BJT?
  8. Shagas
    May 13, 2013
    802
    74
    What 2 wire transmitters?
    Why don't you skip the conversion into a current signal and just use those mV signals from the thermocouple to do what Kubeek suggested?
  9. odinhg
    Jul 22, 2009
    65
    15
    In 4-20mA current loops it is normal to use a 250Ω resistor when you have to convert from 4-20mA into 1-5V (or 500Ω for 2-10V).
    Remember that the transmitters are constant current sources and typically have pretty high compliance voltage.
    The TTH300 temperature transmitter from ABB for example, can drive loads up to (Supply Voltage-11V)/22mA according to its datasheet
    I agree that he can consider leaving out the transmitters and just connecting the thermocouples in parallel to get the average temperature. If the environment allows it (EMC) and he doesn't need the individual temperature measurements. And of course he would need to have a thermocouple input available.
  10. DickCappels
    Aug 21, 2008
    2,756
    665
    If you really have current sources, then just connect all three together and then put a resistor to scale the current to the range you desire, connect the other end of the resistor to the returns for the three current sources and call that point ground.
    You are doing Vo = k (I1 + I2 + I3)
    wayneh likes this.
  11. amitaashu
    Aug 12, 2013
    2 wire transmitter is a tranducer converting physical value ( temperature, level, speed , etc. ) to equivalent electrical signal and having a power source of 24V DC
  12. MrChips
    Oct 2, 2009
    12,624
    3,451
    Depending on the design of the 4-20mA transmitter you could try the following.
    There are two designs of transmitter where the return loop is either on the high side (+24V) or on the low side (GND).
    If the return loop is GND, connect a resistor of about 220Ω, one each for each of the 4-20mA incoming signals. Bring the three resistors to a common node and connect a 33.2Ω resistor from that node to the common return loop (GND) of all three transmitters.
    Now you can read off the average current by connecting a volt meter across the 33.2Ω resistor and measuring the voltage. A reading of 400mV would be equivalent to 4mA average.
    If you want to be precise, use three 100Ω 1% resistors all connected in parallel in place of the 33.2Ω resistor. Mind you there is no appreciable difference between a single 33.2Ω 1% resistor and three 100Ω 1% resistors in parallel.