applying 480 volts to a 440 volt transformer

Discussion in 'General Electronics Chat' started by trognholt, May 20, 2009.

  1. trognholt

    Thread Starter New Member

    May 20, 2009
    1
    0
    I am in the process of hooking a used injection molding press and this machine was rated as a 220/440 volt machine. Our in plant power that I will be applying to thiis machine is 480 volts. That 480 volts is going to be applied to a transformer that is rated for 220/440 that drops the voltage to 100 volts for the controller power. My main questions are concerning the transformer and if this will cause the transformer to burn out and if I will still get the same 100 volt output or will this increase to due the higher applied voltage?
     
  2. mik3

    Senior Member

    Feb 4, 2008
    4,846
    60
    The output voltage of the transformer will be 240V instead of 220V.

    It will not be a problem because transformers are designed to be able to handle voltages around their rated values due to variations in the line voltage.

    Is the voltage stable enough or does it varies a lot?
     
  3. thingmaker3

    Retired Moderator

    May 16, 2005
    5,072
    5
    It will increase due to the higher voltage. At 480V in, the control voltage will be 109V. When the line surges to 500V (which is in keeping with specs for a 480V line) the control voltage will be at 113.6V. If your press controls can tolerate this, there is no issue. Maximum input voltage should be listed in the documentation for your press. If you don't have said documentation and cannot find it online, try contacting the press manufacturer.
     
  4. Slider2732

    Member

    May 6, 2009
    17
    0
    Would be handy if there was an equivalent to logic circuits 7805 type voltage regulators.
    78100 perhaps !
     
  5. mik3

    Senior Member

    Feb 4, 2008
    4,846
    60
    It is an AC voltage, it much complicated to regulate it with solid devices.

    Power companies have taps on the transformers and change them according to the line load.
     
  6. steinar96

    Active Member

    Apr 18, 2009
    239
    4
    Isnt there a risk of core saturation if the voltage per turn is exceeded. Unless the core is made with alot more turns then needed for safety.
     
  7. mik3

    Senior Member

    Feb 4, 2008
    4,846
    60
    There is but I think transformers can tolerate voltages between 10% of their nominal value.
     
  8. THE_RB

    AAC Fanatic!

    Feb 11, 2008
    5,435
    1,302
    Transformers with light loads tend to overheat when the voltage is higher than spec due to the core losses. If your control circuit draws a relatively fixed current it is a typical industrial solution to put a series resistor to the power input to the transformer to drop the voltage 10% or so.
     