4-20mA Signal with HART: ADC Resolution Question

Discussion in 'General Electronics Chat' started by Management, Oct 8, 2009.

  1. Management

    Thread Starter Active Member

    Sep 18, 2007
    306
    0
    Hi Guys,

    HART uses FSK to encode digital information onto 4-20mA analog signals.

    So I have a 4-20mA DC signal that has a sine wave at a frequency of 1200Hz for a 1 or 2200Hz for a 0. The sine wave has a 0.5mA peak (100 peak to peak) on top of the 4-20mA DC signal.

    See this: http://www.smar.com/hart.asp

    What I want to know is will I have enough resolution if I use a 16 bit ADC? Will I have issues with resolving the 1s and 0s? We are doing the filter/separation in the digital domain.

    If not what resolution would I need for signal levels mentioned above?

    Thoughts on this would be great.
     
  2. beenthere

    Retired Moderator

    Apr 20, 2004
    15,815
    282
    That's the hard way. Use a voltage comparator to square up the signals, and feed a triggered counter for a defined period. The number in the counter will tell you if the freq was 1200 or 2200 Hz.
     
  3. Management

    Thread Starter Active Member

    Sep 18, 2007
    306
    0
    From an analog side I don't really care if I have a 1 or a 0. The FPGA will determine that and will be doing a whole bunch of other things.

    I do have a a 250 resistor then Diff. Buffer into the ADC.

    I just need to know if a 16-bit DAC with a 100 kilo-samples per second update will have the resolution.

    Can you help me determine this? Not really a question of how to do it. I really appreciate the suggestion though. And actually would like to talk about it. But just want to answer this question first.

    Thanks.
     
  4. beenthere

    Retired Moderator

    Apr 20, 2004
    15,815
    282
    To resolve a waveform, Nyquist suggested that sampling at at least twice the waveform frequency is necessary. So converting at or above 4400 times/sec will be adequate.

    If all you need is to distinguish between 1200 & 2200 Hz, 8 bits is way more than enough resolution.
     
  5. Management

    Thread Starter Active Member

    Sep 18, 2007
    306
    0
    Yes, but the signal level being so low (1 mA p-p) would that be an issue or would that depend on the ADC?

    Well considering that the current runs across the 250 Ohm resistor and into a Diff. Buffer then the HART would be at about 250mV peak to peak (1200/2200Hz) at the ADC while the 4-20mA would be (in terms of voltage) 1V to 5V.

    Maybe I'm not asking this right but is the 250mV FSK on top of the 1-5V DC too small for an ADC to resolve?

    Thanks again for the help.
     
    Last edited: Oct 8, 2009
  6. Darren Holdstock

    Active Member

    Feb 10, 2009
    262
    11
    It should work OK; the signal levels are perfectly cromulent w.r.t the HART standard, and 16 bits are more than enough.

    The full scale voltage your ADC is referenced to should be 5.125 V or thereabouts*, so 1 bit represents 5.125/65535 = 78 μV (approx). So if the ADC reference is set optimally at 5.125 V then the HART signal will eat up 0.25 V of that, or about 3200 bits. That's more than enough to reconstitute a binary FSK signal.

    *5 V represents the 20 mA, plus (250 mV / 2) for the HART signal makes 5.125 V total. Maybe make the ADC reference a little higher by adding on the noise floor voltage too.
     
  7. Management

    Thread Starter Active Member

    Sep 18, 2007
    306
    0
    Great stuff! Thank you so much.
     
  8. Darren Holdstock

    Active Member

    Feb 10, 2009
    262
    11
    You're welcome Management. Don't take my word for it though, check against the micro datasheet as it may not like an ADC Vref that's bigger than Vdd. Scale everything down if need be.

    You can get a bit more resolution by subtracting the 4 mA level from the signal the ADC sees, though at 16 bits you shouldn't need to. This assumes you're not using sub-4mA levels for special (non-standard) signalling purposes like fault-flagging etc.
     
  9. Management

    Thread Starter Active Member

    Sep 18, 2007
    306
    0
    An ADC has yet to be selected but it is great information to know.

    This is true and can be done but in some cases a requirement that HART be disabled and run 0-20mA. I am assuming that this for fault detection.

    Again thanks for the help. I will update on this because I really do want to mess this up. This being my over project.
     