4-20mA current loop transmitter
Discussion in 'The Projects Forum' started by aaron_tonka, Sep 26, 2013.
  1. aaron_tonka
    Sep 24, 2013
    I am trying to design a 4-20mA current loop for a project. I have a circuit that is nearly working however I cannot get the current below 5.5mA. I attached my circuit. I used an analog devices circuit as a reference which I also attached. The portion of the analog devices circuit I am using starts at R9.
    At 5V input I get a current of 20mA, but at 0V input I get a current of 5.61mA. I have tried changing all of the resistors, and I have tried a couple different op amps with no luck.
    Any help would be appreciated.
  2. wayneh
    Sep 9, 2010
    12,389
    3,245
    What are you using for V1?
    Are you getting more-or-less linear current-vs-voltage but you can't get down to 4mA?
  3. joeyd999
    Jun 6, 2011
    2,757
    2,935
    The LM340 has a quiescent current greater than 5 ma, even at a low 10 mA load. Also, the LM358 is probably running around 2 ma. The total current consumption of the transmitter cannot exceed 4 ma at the max loop voltage, or the transmitter will not work properly.
  4. aaron_tonka
    Sep 24, 2013
    Thanks. I changed the regulator to one with a very low quiescent current and it will now go below 4ma.
  5. joeyd999
    Jun 6, 2011
    2,757
    2,935
    You're welcome.