3 phase bridge
Discussion in 'General Electronics Chat' started by cryosar, Nov 20, 2009.
  1. cryosar
    Thread Starter Active Member
    Apr 2, 2009
    40
    Dear All,
    I have attached the three phase full wave bridge rectifier circuit. I wanted to know how much voltage will appear after the rectification, if the input voltage is 230 V(L-L) & if 230V (L-N). Can anybody tel me the formula and derivation, it will be very helpful to me. Thanks in advance
  2. t_n_k
    Mar 6, 2009
    5,448
    783
    Hi cryosar,
    Never seen that circuit before - certainly not ever as a standard 3-phase bridge. I don't think any current would flow in the neutral link even if you added a DC side load. It might be interesting to simulate the circuit.
    In a standard bridge connection one would expect the neutral either to be floating or acting as a DC side reference point - with the latter connection being the case if you wanted both a positive and negative (dual supply) output on the DC side.
  3. cryosar
    Apr 2, 2009
    40
    Ok
    Can you give me the formula for the circuit without connecting neutral?
  4. aboamal
    Member
    May 29, 2008
    14
    the circuit must be like this
    and the output of dc formula as following
    Vdc=Vac(3 phase)X1.3
  5. cryosar
    Apr 2, 2009
    40
    This is for 1 phase AC circuit
  6. cryosar
    Apr 2, 2009
    40
    But the measured value is not matching with the formula
  7. rjenkins
    Nov 6, 2005
    1,015
    69
    If that circuit was used two series smoothing capacitors, with the centre point of the caps to neutral, it would give the same output whether operating on a single phase or a three phase supply.
    The output should be about double the peak of a single phase. In effect, any phase feeds two half wave rectifiers, one to positive and one to negative.
    The two diodes to neutral would prevent either smoothing cap being reverse biassed as the load discharges them after the supply is removed.
    Without the neutral link to the smoothing caps, the output should be the peak of the phase-to-phase voltage and it would work as a basic 3 phase (only) rec.
  8. t_n_k
    Mar 6, 2009
    5,448
    783
    Just to complete this ....
    Vdc = 2.34Vs
    where Vs is the line-to-neutral voltage
    If using line-to-line voltage [VL]
    Vdc= 1.35VL
  9. cryosar
    Apr 2, 2009
    40
    The measured values are for Line to neutral voltage Vs= 49V the Vdc is 57V
    The measured values are for Line to Line voltage Vs= 49V the Vdc is 116V