    I need a three phase AC to single phase AC, 50 Hz converter of 15-20kVA rating with sine wave output. I couldn't find it readily available in market nor could get good response in google.. Are such converters available ? Pls suggest.
     
  2. inwo

    Well-Known Member

    Nov 7, 2013
    2,433
    315
    What type of load?

    Most single phase loads can be balanced across 3 phases.
     
  3. BR-549

    Well-Known Member

    Sep 22, 2013
    1,995
    388
    May we know what you are powering with the single phase? What is the voltage of the 3 phase input? What voltage are you looking for in the single phase output?
     
  4. MaxHeadRoom

    Expert

    Jul 18, 2013
    10,548
    2,373
    A 3ph transformer is made up of three single phase transformers.
    Why not just install a suitable sized 1ph Txfmr across two of the incoming phases?
    What are you feeding it from?
    Max.
     
  5. MrAl

    Well-Known Member

    Jun 17, 2014
    2,433
    490
    Hi,

    Wow, 20kW from single phase is a lot of current. Even at 220vac that's around 91 amperes. That's why 3 phase works better for huge loads like that.
     
  6. tcmtech

    Well-Known Member

    Nov 4, 2013
    2,035
    1,660
    I suggest reading up on 'Zig Zag' or 'Z' connected systems. They are the easiest way to get a large single phase load to balance out over a three phase feed source.

    Personally I don't consider 20 KW on single phase top be all that big. The primary feeder for my place is a 200 amp 120/240 single phase.
     
    MaxHeadRoom likes this.
  7. DNA Robotics

    Member

    Jun 13, 2014
    123
    26
    Just use 2 of the 3 wires and you will have single phase.
     
  8. MrAl

    Well-Known Member

    Jun 17, 2014
    2,433
    490

    Hi,

    Are you telling me that you would not mind loading your 120vac line with 20kW from one single application device? That's 167 amperes, assuming it is a purely resistive load. If it's not purely resistive, it could be much worse.

    Also, connecting to one phase of a three phase system could cause a big imbalance in the three phase system.

    When is the last time you ran something this huge :)
     
  9. alfacliff

    Well-Known Member

    Dec 13, 2013
    2,449
    428
    wouldnt it be advisable to find out if the 3 phase is delta or wye connected?
     
    Last edited: Jun 25, 2014
  10. MaxHeadRoom

    Expert

    Jul 18, 2013
    10,548
    2,373
    I also have a 1ph 50kVA transformer sitting at the end of my yard feeding a 200amp service to the house and shop, apart from the usual domestic load, I also have a small machine shop with CNC machines and a 50amp outlet for a welder.
    The OP did not mention if this was for a singular load, as he is posting from India the normal domestic supply is 220v.
    Max.
     
  11. tcmtech

    Well-Known Member

    Nov 4, 2013
    2,035
    1,660
    Well my big plasma cutter pulls around 135 amps at 240 VAC plus I have a 15 HP air compressor that cycles on and draws 100 - 120 amps on start up along with all my normal home and shop background loads. So yes for me seeing 40+KW/KVA or higher loads at my place is trivial at best.

    Personally around here seeing newer farms and larger rural homes with 400 and 600 amp 120/240 VAC services is pretty normal here.

    A buddy of mine built a new shop a few years ago with all electric heating on top of his all electric heat in his house so his service was upgraded to a 600 amp system with a 100 KVA transformer feeding his place.
     
  12. MrAl

    Well-Known Member

    Jun 17, 2014
    2,433
    490
    Hi,

    Wow that's amazing. Here we are lucky if we have 200 amp service, and that's when it works right.

    Factories around here of course have better.
     
  13. inwo

    Well-Known Member

    Nov 7, 2013
    2,433
    315
    200 amps was enough for me when I build my home, but 40 circuits is never enough.

    So I went to 400A rather than a sub-panel.
     
  14. vks_foe

    Thread Starter Active Member

    Jan 11, 2009
    55
    5
    Pls explain. I have only one load which is single phase 15kva..
     
  15. vks_foe

    Thread Starter Active Member

    Jan 11, 2009
    55
    5
    It is an inductive load with pf >0.9. Input : 415 ph-ph. o/p : i need variable ac (0-1250V, 50Hz)
     
  16. vks_foe

    Thread Starter Active Member

    Jan 11, 2009
    55
    5
    This is what I was worried about. I donot want to create an imbalance in the system. So i thought of buying a solid state converter which has 3 phase 415V ac input and single phase AC output which is variable.

    BTW, how much load imbalance is generally allowed, I mean if i'm loading a phase with 15kVA, what should be the minimum rating of the feeding transformer that this becomes negligible (or acceptable)?
     
  17. tcmtech

    Well-Known Member

    Nov 4, 2013
    2,035
    1,660
    Personally I would not worry about phase imbalance unless you are running at over 50% of what the primary three phase supply transformer is rated for phase to phase for extended periods.
    Which if its a utility owned and operated unit supplying power to multiple customers or the like the odds are its pretty robustly built and even that much of a imbalance is not likely going to cause any substantial problems on the other lines.

    15 KVA may sound like a lot to you but on the utility scale of things its trivial at best.
     