3 phase 4 wire system will make me mad!

Discussion in 'General Electronics Chat' started by s2pk, Jun 29, 2012.

  1. s2pk

    Thread Starter Member

    Jul 10, 2010
    77
    0
    let say we have cable ampacity of 100 Amps, and load connected to all three wires is 50Amps, so the neutral wire (return path) have to carry the current of all three live wires (150Amps). Now my question is how the neutral wire carries current greater than its ampacity???
     
  2. gerty

    AAC Fanatic!

    Aug 30, 2007
    1,153
    304
    Neutral is designed to carry UNBALANCED LOAD, if all 3 phases are carrying 50 amps like you say there should be no load on neutral.
    I'm sure all the loads are not exactly the same, so there will be some current on neutral.
     
  3. GetDeviceInfo

    Senior Member

    Jun 7, 2009
    1,571
    230
    just restating the previous post;

    the current in the phases add together at the common neutral point. If balanced, vectorally, the sum is zero, hence no flow in the neutral.
     
  4. s2pk

    Thread Starter Member

    Jul 10, 2010
    77
    0
    I am not satisfied with your answer plz elaborate, I found different currents on all phases and neutral wire showed the sum of currents on all phases. So if current on R, Y, B is say 98, 99, 100 amps respectively it means neutral will show reading of 98+99+100. How neutral wire can carry current greater than its ampacity ???
     
  5. BillB3857

    Senior Member

    Feb 28, 2009
    2,400
    348
    You actually measured the sum of the individual phase currents on the neutral???????? Show us a diagram of what you have connected and how it is connected.
     
  6. GetDeviceInfo

    Senior Member

    Jun 7, 2009
    1,571
    230
    Start here;
    http://www.allaboutcircuits.com/vol_2/chpt_2/1.html
     
  7. s2pk

    Thread Starter Member

    Jul 10, 2010
    77
    0
    I will post the screenshot tomorrow
     
  8. cork_ie

    Member

    Oct 8, 2011
    348
    58
    If three men have three ropes and one end of each rope is connected to a small circular ring. If they pull the ropes in three different directions separated by 120 degrees , the power (rate of doing work) required to hold the ring at a fixed point will be the net of the power supplied by each of the three men, not the three added together. If each man was pulling equally there would be zero net pulling force.
    While current flow does not initially appear to be analogous to work, energy (and power) they are similar whether mechanical or electrical.
     
  9. takao21203

    Distinguished Member

    Apr 28, 2012
    3,577
    463
    yes the ring itself would not move, but there is still tension between the individual ropes. Isn't it true in a balanced AC circuit (for 3 phase) the N wire can be omitted altogether?
     
  10. strantor

    AAC Fanatic!

    Oct 3, 2010
    4,302
    1,988
    I have seen 3 phase heaters and motors do not have a neutral. They have a green earth ground but not a neutral.
     