277 volt lighting / transformer

Discussion in 'Off-Topic' started by Erin G., Mar 3, 2005.

  1. Erin G.

    Erin G. Thread Starter Senior Member

    Joined:
    Mar 3, 2005
    Messages:
    167
    Location:
    Missouri, USA
    I work at a plant that uses three phase, three wire power. None of the three phase transformers are grounded. The transformer in question is a 2400 to 480 volt AC, delta - delta.

    We ordered some 277 volt light fixtures that will not work. A co-worker is sure that since you can measure 277 VAC from any one leg of the three phase to ground, then you should be able to hook up a 277 volt lighting ballast, one side of the ballast to a phase, the other to ground, and the light will work. When we actually do this our 277 volts to ground drops to 159 volts. The more lights we put in the circuit, the more the voltage drops. I'm pretty sure that a transformer has to have it's own reference to ground (center tap to ground on wye, H1 on delta) before you can get a usable 277 volt power supply.

    If I'm wrong, why wont our lights work? If I'm right, how do I explain this to my co-worker?
  2. mozikluv

    mozikluv AAC Fanatic!

    Joined:
    Jan 22, 2004
    Messages:
    1,437
    Location:
    Philippines
    hi erin

    sorry i can't give you a descent answer to your query, but you should repost this at the General Electronics Chat. am sure you will have what you want to know. or you can PM "Bipin". he is an electrical engineer. :)
  3. pebe

    pebe Distinguished Member

    Joined:
    Oct 11, 2004
    Messages:
    620
    Location:
    Scotland

    You are quite right. Your lights require a single phase supply, but you cannot get that from a Delta wired transformer, because there is no neutral connection. You need a Star connected transformer.

    A possible way to get single phase might be to connect a Star 3phase tranforner to the 3 phases to create a neutral, but I'm not sure. Another way would be to use a 480v/277v autotransformer.

    Or you could wire two (equal wattage) lamps in series across the 480v phases and run them at slightly reduced brightness.
  4. Erin G.

    Erin G. Thread Starter Senior Member

    Joined:
    Mar 3, 2005
    Messages:
    167
    Location:
    Missouri, USA
    Thanks for the response. I found some helpful schematics at www.kilowattclassroom.com, but apparently my co-worker did the same research, because he wasn't in the mood to debate the subject any further.

    Fortunately, the existing ballast has a multi-tap primary, with a 208 volt lead available. We were able to get 208 VAC from the delta secondary feeding the circuit to the lighting ballast without any significant increase in amps.
  5. JayTech

    JayTech New Member

    Joined:
    Mar 26, 2005
    Messages:
    1
    You are right in that to use the apparent 277VAC which you sometimes see on one leg (any one leg) of the transformer,
    you must have a neutral reference which is valid.
    A DELTA output has NO valid neutral. THAT IS why it is a delta and not a 'wye'.
    It is a triangle shape symbol for its output windings, and only provides a stable predictable usable power output when taking any two legs to obtain a single phase voltage (which will be 480 volts); (or all three legs for three phase).
    The fact that you observed 277 volts is a coincidence of luck (good or bad you pick). Ground is a meaningless (or better to say ambiguous to the unwary) place to return your meter lead to, and read a valid voltage, on a delta winding, since the delta winding doesn't reference to ground (it is unconnected to it).
    I can ground my meter lead to my ankle and read all kinds of weird voltages from circuits if I choose, but none of the readings observed will have any validity to an AC power circuit. I will get readings though.
    BE wary of readings obtained with sensitive electronic meters, as they will give indications based on leakage currents and weak / non-existant / non-wired return paths.
    The proof that it is not a valid power output voltage is: that when you load it, it goes down so much, with not even an appreciable load.
    A valid load on a valid lighting transformer would barely cause a drop in voltage (maybe 5 percent) with normal load factor.
    If you want to use that transformer, you must buy single phase 440 volt ballasts.
    If you want to use the 277 volt ballasts, buy a transformer that has a delta primary (440 volt); Connect it to the load side of your existing 440 volt delta transformer, and your new transformer must provide a wye-configured output, rated at 277 volt (each leg to neutral of the wye) output secondary.
    If it is still unclear what is going on, email or post again.
    JayTech.
  6. Buddrow

    Buddrow New Member

    Joined:
    Mar 14, 2008
    Messages:
    1
    Hi
    Can you tell me where to get the schematic for this setup. I have a customer who has a similar problem and he insist the multitap ballast will not work.

    thanks
    Buddy

    EDIT: Keep the discussion on the forums, or request a contact through PM. Posting your URL up in this way constitutes advertising. Thank you - Dave
  7. Dave

    Dave Senior Member Staff Member

    Joined:
    Nov 17, 2003
    Messages:
    6,961
    This thread is nearly 3 years old. It is unlikely you will get any assistance on this matter.