20A current transformer Amecon 5304
Discussion in 'General Electronics Chat' started by superway, Sep 16, 2013.
  1. superway
    Thread Starter Active Member
    Oct 19, 2009
    128
    How to test and verify a 20A Current Transfomer ( p/n Amecon 5304) is accurate reading? Because we found out a lot CTs read not accurate Amps when applied a low current 1A on it and compared the current between measurment (by current probe) and display ( on our Microboard). So that, we have to test every single CT first before installing on PCBA board.
  2. t_n_k
    Mar 6, 2009
    5,448
    783
    What current waveform are you measuring or monitoring with the CT? Purely sinusoidal?
  3. shortbus
    Sep 30, 2009
    4,092
    1,674
    Are you using the CT in the way shown on the data sheet?
  4. superway
    Oct 19, 2009
    128
    Hi Shortbus,
    Yes that's correct the picture.
    I used both measurments, scope (sinewave) and power meter to monitor the number.
  5. MaxHeadRoom
    Jul 18, 2013
    10,836
    2,510
  6. crutschow
    Mar 14, 2008
    13,482
    3,370
    What is the maximum current you need to measure? If less than 10A, you can increase sensitivity (and accuracy) by adding more primary turns, as Max noted.
  7. #12
    Nov 30, 2010
    16,671
    7,314
    That's a slick trick I use with a clamp meter. Ten turns around the arm of the clamp and a couple of alligator clips make a 6/10 amp scale to measure relay control current.
  8. superway
    Oct 19, 2009
    128
    This is fixed current transformer, please see picture AMECON 5304. I can't add more turns on it. The current i measured is 1A ( the turns ratio of CT: 1000:1). Thanks
  9. #12
    Nov 30, 2010
    16,671
    7,314
    They are talking about the .355 inch diameter hole in the center. If you can run the current carrying wire through the hole more than once, you can get a different turns relationship. If you are only measuring 1 amp, that can be done with a pretty small wire and you can get several turns of it through the hole.
  10. shortbus
    Sep 30, 2009
    4,092
    1,674
    What I was talking about was the 100 Ohm load resistor across the secondary outputs of the transformer. Then you measure the voltage from that. Kind of like a Kelvin/4 point measurement.
  11. shortbus
    Sep 30, 2009
    4,092
    1,674
    Like shown on the first page of the data sheet
  12. superway
    Oct 19, 2009
    128
    Hi Shortbus,
    I can set my variac AC source to 60Vac, then connect the LINE through CT donut and out to a power resistor 60 Ohm/250W. The NEUTRAL from variac connects to another end of power resistor. So that I can measure 1amp ac from primary, and the voltage (0.1V per Amp) from secondary.
    Any advise.
  13. shortbus
    Sep 30, 2009
    4,092
    1,674
    The CT has to be used as shown in the data sheet. I circled in red the schematic from the page. Below the schematic is a graph showing the different voltage out puts that can be expected for different load resistor values.
    The Circuit you are using the CT in MUST have a load resistor in it for the CT to work as expected. If the circuit doesn't have the load resistor, it is not going to work reliably. If you don't have the load resistor in the circuit, this is probably why you are having so many failures in the product. CT are pretty simple and not prone to failure, can't believe they are bad from the factory.
      File size:
      306.3 KB
      45
  14. superway
    Oct 19, 2009
    128
    Oh yes, I have a 100 ohm 1/4W load in secondary CT. Those CTs are not bad, the reason I try to measure is looking for CTs have more accurate reading voltage on secondary when applying small current 1A thru the donut. Some of 20A CTs have not accurate reading at lower amp, but to be more accurate at higher amp like 10A or 15A.