14 VDC power supply putting out 24 VDC
Discussion in 'General Electronics Chat' started by Johnnyb60, Mar 15, 2015.
  1. Johnnyb60
    Sep 6, 2013
    30
    I’ve been having some problems with some circuits and decided to check the supply voltage to find 24VDC. I’ve had this power supply for over 25 years and did have some circuit cards connected to this power supply fail about 6 or 7 years ago, but I can’t remember if I checked the power supply voltage at the time. I know the voltage will be a little high until a load is applied, but I just don’t remember it being this high.
    Anyway I pulled off the cover to see if there might be an adjustment someplace and there isn’t anything. There are a couple of large resistors on the output of the transformer and wondering if they might be going bad. I haven’t actually measured the resistance and I don’t have a schematic, but I just wanted to run it by someone who knows this stuff before I start tearing it apart.
  2. Papabravo
    Feb 24, 2006
    10,338
    1,850
    Is it a linear supply or a switching supply?
    What is the AC output of the transformer?
  3. Brevor
    Apr 9, 2011
    282
    56
    can you post a picture of the nameplate that shows what the output voltage should be?
  4. mcgyvr
    Oct 15, 2009
    4,787
    973
    Its common for an unregulated supply to output voltage higher than its rating when unloaded..
  5. BReeves
    Member
    Nov 24, 2012
    412
    64
    The photo doesn't really show enough to be able to tell a whole lot. Need the other side, maybe the top of that circuit board, name plate and rear.
  6. Johnnyb60
    Sep 6, 2013
    30
    The transformer is AC output and uses a fullwave bridge inside the enclosure for DC. I don't know about a switching supply. It is a Motorola power supply for 12 volt radios.
  7. Johnnyb60
    Sep 6, 2013
    30
    and
  8. Johnnyb60
    Sep 6, 2013
    30
  9. Papabravo
    Feb 24, 2006
    10,338
    1,850
    Well I wanted you to tell me what the AC output voltage of the transformer was. If the supply is not a switcher which seems likely given it's age and application then 24V on the output would be a bad bad thing. There is a failed component that is allowing the input to the regulator to pass through to the output. If the AC output is about 18VAC, then multiplying by 1.414 is 25.5VDC from which we subtract the bridge drop of 1.5 V to get 24VDC out of the bridge rectifier.
    Johnnyb60 likes this.
  10. MrChips
    Oct 2, 2009
    12,624
    3,451
    Firstly, check your voltmeter against a know voltage source such as a 9V or 12V battery.
    If the meter checks out ok then it looks like the pass transistor is shorting.
  11. Johnnyb60
    Sep 6, 2013
    30
    I don't know which one is the pass transistor. Is it one or both of the big ones in the huge heat sink shown in the last photo?
  12. MikeML
    Oct 2, 2009
    5,450
    1,066
    MrChips and Johnnyb60 like this.
  13. MrChips
    Oct 2, 2009
    12,624
    3,451
    You have two in that unit, the big ones on the heat sinks marked M9639.
    Remove both transistors and measure the resistance from collector to emitter.
  14. Johnnyb60
    Sep 6, 2013
    30
    WOW that's fantastic! I can't thank you enough MikeML :) The schematic is a big help and I think I can now make some checks.
  15. Johnnyb60
    Sep 6, 2013
    30
    Thanks I think I'll be able do that much :)
  16. MikeML
    Oct 2, 2009
    5,450
    1,066
  17. Johnnyb60
    Sep 6, 2013
    30