  #1  
Old 06-08-2006, 08:09 AM
chyau chyau is offline
New Member
 
Join Date: Jun 2006
Posts: 1
Default

i'm from malaysia. my country's electrical standard voltage is 240V,50Hz.
i'm working as a trainee in a construction site now..
i'm wonder how many 36w fluorescent light can be connected seriesly in a circuit by using a 1.5mm cable or 2.5mm cable?
what will happen if the cable limitation was exceeded??
which formula we should apply in this situation or we need the cable characteristic also??

thank you for answering my Q.
Reply With Quote
  #2  
Old 06-08-2006, 08:46 PM
Papabravo's Avatar
Papabravo Papabravo is online now
Senior Member
 
Join Date: Feb 2006
Location: Michigan, USA (GMT-5)
Posts: 5,786
Default

Quote:
Originally posted by chyau@Jun 8 2006, 04:09 AM
i'm from malaysia. my country's electrical standard voltage is 240V,50Hz.
i'm working as a trainee in a construction site now..
i'm wonder how many 36w fluorescent light can be connected seriesly in a circuit by using a 1.5mm cable or 2.5mm cable?
what will happen if the cable limitation was exceeded??
which formula we should apply in this situation or we need the cable characteristic also??

thank you for answering my Q.
There are tables which give the current carrying capacity of various types of wire. In the US they are in English Units which won't help you too much. I suspect there are similar tables for wire with metric dimensions. The concept is that given the wire diameter and construction you can find the resitance per foot(meter), then you can compute a power dissipation for a wire of length l, in watts. This power dissipation will lead to a temperature rise which we desire to limit.

Example:

1.5 mm is halfway between 14 guage and 15 guage which handle 5.87 and 4.66 Amps respectively.

2.5 mm is pretty close to 10 guage wire which can handle 14.8 Amps.

12-14 guage wiring is typical for US residential construction

Hope this helps
__________________
We never have time to do it right,
But we always have time to do it over.
Reply With Quote
  #3  
Old 06-09-2006, 08:59 AM
Gadget Gadget is offline
Senior Member
 
Join Date: Jan 2006
Location: Queenstown, New Zealand
Posts: 613
Send a message via MSN to Gadget
Default

A note to our US readers, gauges required for 230 - 240V distribution are considerably lighter than for a similar 110 - 120v setup.

Generally either 1mm or 1.5 mm TPS is used for 240v lighting, and is on a 10A breaker. Run Distance is obviously also a factor. If a 10 Amp load (2.4KW) were Right at the very end of a 50m 1.5mm cable run, then the max allowable voltage drop would be exceeded.
In a hall situation several of these circuits are normally run out with the loading placed all along the run (not normally right at the end) so that lighting is more controllable, and also so that excess load isn't put on one circuit.
2.5 mm TPS is normally looped to a few 10A wall outlets with a 25A breaker on each run.
Unsure if your regs are the same as ours, but they are probably similar.
As a tech, and not one of the "sparkies" in our firm, I cant answer much more than that, But I think the Max Voltage drop allowable in a cable run here is 5% (or 11 - 12V).

Most cable manufacturers have Tables or calculators available for supply voltage, allowable VD%, length, current vs Cable size and type.

Calculator

Cable calculator
Reply With Quote
Reply   Post New Thread

Tags
, , , ,


Similar Threads
Thread Thread Starter Forum Replies Last Post
USB device cable shield connection - grounding it or not? colinb General Electronics Chat 11 08-30-2011 08:26 PM
Faulty Electrical causing slow Internet speeds march09 Computing and Networks 7 11-12-2009 06:34 AM
Need Electrical Design Simulation and Calculation Tools stfelton Electronics Resources 10 11-04-2009 11:10 PM

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 01:28 PM.


User-posted content, unless source quoted, is licensed under a Creative Commons Public Domain License.
Powered by vBulletin
Copyright ©2000 - 2014, vBulletin Solutions, Inc.