Default How is it that there is continuity and a voltage reading yet no short circuit?

Excuse me if I don't explain this correctly. I am trying to get my head around how this works. Please ask for clarifications and I will do my best to do so.

My question is about how is it that when I do a voltage check from line side to load side at a meter box with a main breaker switch closed that I will get 120V and that I will get a beep when doing a continuity test yet there isn't a short in the system to allow a complete circuit?

If there is nothing plugged into the walls of a residence, how is it that there is a circuit for the voltage reading and continuity test to occur?

See my diagram below. At the wall outlet, there is an open break in the circuit until a load is plugged in. How then am I getting these results when I do my test before the main breaker when nothing is plugged into the wall outlets in the entire residence?
I was told it was because of the ground wire at the outlets. But that makes me think that that would actually be a short circuit if that was the case and we'd have continuous electrical usage...

::"image removed due to hosts image bandwidth constraints"

Thanks in advance for any explanations.

Last edited by foolios; 01-23-2010 at 02:15 PM.
Reply With Quote
  #2  
Old 02-05-2009, 04:14 AM
Audioguru Audioguru is offline
Banned
 
Join Date: Dec 2007
Location: Ontario, Canada
Posts: 9,411
Default

A breaker is not "opened or closed". It is turned on or it is turned off.
If the breaker is turned on then of course voltage is at the wall outlet even if nothing is plugged in to draw current.

A continuity tester tests wires that are not powered, the breaker must be turned off.
Reply With Quote
  #3  
Old 02-05-2009, 04:26 AM
SgtWookie's Avatar
SgtWookie SgtWookie is offline
Expert Member
 
Join Date: Jul 2007
Location: In the vast midwest of the USA; CST
Posts: 21,989
Default

Ground is connected to Neutral at the main breaker panel. In most normal circumstances, this is the only place that the two meet.

Outside the residence, usually right near the electrical service entrance, there are one or two 8' long copper-clad stakes driven into the ground, with an AWG 4 or larger conductor clamped to it. This usually gives a reliable earth ground for many years.

This conductor is run to the main service panel, and attached to the ground buss. There is a separate Neutral buss, however the two are tied together. This keeps the line voltages from rising to very high levels, should a fault occur in the power company's transformer; the transformer's fuses will blow instead of creating a very dangerous situation.

Although Ground is connected to Neutral at the service panel, the ground wire should never be used to carry return current to the service panel. The ground wire is there to provide safety for the human users of the electrical service; the chassis of appliances are connected to the ground wires to protect them from an internal fault.

GFCI (Ground Fault Circuit Interrupt) breakers such as used in kitchen, bathroom and outdoor recepticles detect current flow in the ground circuit, and will open the circuit (trip the breaker) if the current in the ground wire exceeds around 15mA.
__________________
General info:
If you have a question, please start a thread/topic. I do not provide gratis assistance via PM nor E-mail, as that would violate the intent of this Board, which is sharing knowledge ... and deprives you of other knowledgeable input.
Reply With Quote
  #4  
Old 02-05-2009, 09:51 AM
studiot's Avatar
studiot studiot is offline
E-book Developer
 
Join Date: Nov 2007
Location: Somerset UK
Posts: 3,733
Default

Quote:
how is it that there is a circuit for the voltage reading
Please remember that you need a circuit for current to flow, but not for voltage to be present.

Think about an ordinary battery there is always voltage between the terminals (for a good one), whether it is connected into a circuit or not.
__________________
Do I look old?
I don't feel old.
I don't feel anything till noon.
Then it's time for my nap.
Reply With Quote
  #5  
Old 02-05-2009, 11:17 AM
mik3's Avatar
mik3 mik3 is offline
Senior Member
 
Join Date: Feb 2008
Location: Cyprus, but now in UK (GMT+0)
Posts: 4,846
Blog Entries: 9
Default

Where do you place the meter probes when you perform the voltage measurement and continuity test?
Is the main braker turned off during tests?
Reply With Quote
  #6  
Old 02-05-2009, 11:40 PM
foolios foolios is offline
Member
 
Join Date: Feb 2009
Location: U.S.
Posts: 80
Default

Quote:
Originally Posted by mik3 View Post
Where do you place the meter probes when you perform the voltage measurement and continuity test?
Is the main braker turned off during tests?
I am placing the meter probe from the line side of the meter box(the jaws in it) to the load side of the meter box.

What I test for is to make sure that the main circuitbreaker is off(open).
What I want to understand is:
If the main switch is closed(on) and there is nothing plugged into any outlet in the residence and there is nothing on that would draw current, would I get a voltage reading? If so, why?
How can there be a voltage reading if there is nothing plugged in or on to be powered up/complete the circuit if that's so?

Also, in this same scenario, would a continuity test be possible? As I read above, continuity tests can only be done with the power off, so in this case of a main closed, would that mean a continuity test can't be done even though there is nothing plugged in to complete the circuit?

THanks for the replies.
Reply With Quote
  #7  
Old 02-05-2009, 11:50 PM
mik3's Avatar
mik3 mik3 is offline
Senior Member
 
Join Date: Feb 2008
Location: Cyprus, but now in UK (GMT+0)
Posts: 4,846
Blog Entries: 9
Default

If the main breaker is turned on there will be a voltage between neutral and live wires on the outlet. The voltage on the outlet does not depend on the appliance connected to it but it always there and waits to power an appliance. When an appliance is connected it will draw some current and this current depends on the power of the device. Don't confuse voltage with current.

As for the continuity test don't make it with power on, you may get shocked or blow the meter.
Reply With Quote
  #8  
Old 02-05-2009, 11:58 PM
beenthere's Avatar
beenthere beenthere is offline
Senior Member
 
Join Date: Apr 2004
Location: Missouri, USA (GMT -6)
Posts: 15,815
Blog Entries: 10
Default

If you are looking for continuity under the stated conditions -
Quote:
My question is about how is it that when I do a voltage check from line side to load side at a meter box with a main breaker switch closed that I will get 120V and that I will get a beep when doing a continuity test yet there isn't a short in the system to allow a complete circuit?
then you have to read continuity. Having the breaker closed means it is acting like a switch that is turned on. Checking from one side of it to the other will naturally show continuity.

One verifies the state of a breaker by looking for voltage between the hot lead and its associated neutral. If you still see 120 VAC, the breaker is closed. If open, the voltage will not be present.

Checking continuity is done on circuits which have been disconnected from the power source. If you suspect an open, the check may be done with a voltmeter and power on. You place a lead at the source and probe with the other. Finding a spot where the source voltage is read means there is an open between the metered points.
__________________
First comes the hardware, then the software.
Reply With Quote
  #9  
Old 02-06-2009, 12:41 AM
foolios foolios is offline
Member
 
Join Date: Feb 2009
Location: U.S.
Posts: 80
Default

I need to break this down a little. Lemme isolate just the voltage concerns.
When I test for voltage at the meter box and the breaker is open, I get no reading. Now, isn't there potential for voltage right here at the box just like if the breaker was closed and there was nothing plugged into the wall outlet; which makes this the same test when I'm also testing for voltage at the wall outlet? There is a break isn't there? Whether it's at the open main or whether it's at the open wall outlet. I don't understand how it is any different between the two when it comes to reading potential voltage.

As far as if it's about completing a circuit, of which is where I believe my misunderstanding lies.
I can see if there was an appliance that was plugged in and on. This completes a circuit. I should get a voltage reading. Voltage wants to push current.
But how is this occuring when there isn't an appliance plugged in and on to complete the circuit? Yes, there is a neutral connected to each outlet but it's not directly connected, otherwise there would be a short.

Sorry if I'm beating a dead horse, I really am curious to understand at least this part of it.
Reply With Quote
  #10  
Old 02-06-2009, 12:54 AM
beenthere's Avatar
beenthere beenthere is offline
Senior Member
 
Join Date: Apr 2004
Location: Missouri, USA (GMT -6)
Posts: 15,815
Blog Entries: 10
Default

The situation is very like an earlier example, where you can see voltage across a battery in the absence of any circuit than the meter. That is like reading 120 VAC at an outlet that is otherwise open. The voltage is just the difference in potential between the hot wire and the neutral.

If you open the breaker feeding that branch, the voltage goes away at the outlet, and at every other part of that branch.

If I understand this -
Quote:
Now, isn't there potential for voltage right here at the box just like if the breaker was closed and there was nothing plugged into the wall outlet; which makes this the same test when I'm also testing for voltage at the wall outlet? There is a break isn't there? Whether it's at the open main or whether it's at the open wall outlet. I don't understand how it is any different between the two when it comes to reading potential voltage.
- you have read across an open breaker and see voltage. With a high impedance voltmeter and a bit of leakage in the branch, that's not too surprising. Plug in any load, though, and that voltage will go away.
__________________
First comes the hardware, then the software.
Reply With Quote
Reply   Post New Thread

Tags
, , , ,


Related Site Pages
Section Title
Textbook Safe practices : Electrical Safety
Worksheet Overcurrent protection
Worksheet Lock-out / Tag-out
Worksheet Safety grounding
Video Lecture Troubleshooting Series Circuits - Circuit Troubleshooting
Textbook Transformer -- power supply : Ac Circuits
Textbook Fuses : Physics Of Conductors And Insulators
Textbook Safe circuit design : Electrical Safety
Textbook Common sources of hazard : Electrical Safety
Textbook Safe meter usage : Electrical Safety


Similar Threads
Thread Thread Starter Forum Replies Last Post
No current through ammeter in simple battery circuit GreenPenInc The Projects Forum 10 01-11-2010 01:29 AM
power supply short circuit protection, overcurrent draw relicmarks General Electronics Chat 22 11-05-2008 01:47 AM
LOW VOLTAGE Circuit TESTER lamps relicmarks General Electronics Chat 5 11-03-2008 12:32 AM
Shorts with a negative supply relicmarks General Electronics Chat 40 04-16-2008 02:22 PM

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 11:23 PM.


User-posted content, unless source quoted, is licensed under a Creative Commons Public Domain License.
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2014, vBulletin Solutions, Inc.