Default what is the difference between neutral and ground ??

please tell me the difference between the two
Reply With Quote
  #2  
Old 09-16-2008, 03:40 PM
scubasteve_911 scubasteve_911 is offline
Senior Member
 
Join Date: Dec 2007
Posts: 1,202
Default

It can be stated that Neutral can be grounded, but Ground is not neutral.

A Neutral represents a reference point within an electrical distribution system. Conductors connected to this reference point (Neutral) should, normally, be non current carrying conductors, sized to handle momentary faults (short circuits) occurring in electrical equipment. However, with the introduction of non linear loads, such as computers, electronic lighting, TVs, VCRs and other switchmode power conversion equipment, the requirements for the neutral conductor has changed (increased).

A Ground represents an electrical path, normally designed to carry fault current when a insulation breakdown occurs within electrical equipment. (Note: Breakdowns can be forced by connecting (dropping) a metal tool or conductive material from a voltage potential to the steel structure within a facility.) Connections to the electrical path (Ground) are made convenient for the installation of electrical equipment. Some current will always flow through the ground path. This current will come from a number of normal sources. Capacitive coupling and Inductive coupling between power conductors and the ground path (conductive conduit, conductive structure members, etc) are the greatest sources of ground path current.

Source: http://www.ab.com/drives/techpapers/rfignds.htm

also http://en.wikipedia.org/wiki/Neutral_wire is good
Reply With Quote
  #3  
Old 09-17-2008, 12:59 AM
SgtWookie's Avatar
SgtWookie SgtWookie is offline
Expert Member
 
Join Date: Jul 2007
Location: In the vast midwest of the USA; CST
Posts: 21,994
Default

Scubasteve,
I have exceptions with your post.

In a "normal" AC service, the neutral provides the return path for current on the 120v sides, and has no function for 240v appliances.

"Ground" should never have any current on it. If there is more than a few mA current on a "ground" wire, there is a problem.

The purpose of the Neutral wire is a power return path.

The purpose of the Ground wire is for operator safety.

At the electrical service panel, Neutral and Ground are connected together. This must be the only place that they meet, or the premise of human safety is violated.

No, I'm not an electrician. However, this is a very important issue. I hope that someone who IS a licensed electrician will respond to this thread, and confirm or correct my assertion.
__________________
General info:
If you have a question, please start a thread/topic. I do not provide gratis assistance via PM nor E-mail, as that would violate the intent of this Board, which is sharing knowledge ... and deprives you of other knowledgeable input.
Reply With Quote
The Following User Says Thank You to SgtWookie For This Useful Post:
#12 (10-03-2013)
  #4  
Old 09-17-2008, 02:51 AM
scubasteve_911 scubasteve_911 is offline
Senior Member
 
Join Date: Dec 2007
Posts: 1,202
Default

Well, I actually just copied and pasted from that website to make it easy, which I stated the source. I'm glad I am not under the Wookie-glass !

Steve
Reply With Quote
  #5  
Old 09-17-2008, 04:16 AM
thingmaker3's Avatar
thingmaker3 thingmaker3 is offline
Super Moderator
 
Join Date: May 2005
Location: Rural, Oregon GMT -8
Posts: 5,072
Blog Entries: 6
Default

I'm licensed in Oregon and Washington and am a member of IBEW Local 48.

The notion of neutral and ground is indeed a confusing one, primarily because of unfortunate terminology.

First, a word to all those who oppose the phrase "current flow:" Buzz off! I am not going to further complicate this SAFETY issue with the phrase "charge flow." The terms "current" and "charge flow" and "current flow" all mean the same thing. If you don't like it, stop reading NOW.


"Current carrying" does not mean the same thing as "conducting." "Current carrying" is more like "hot" or "switched hot" or "traveler." Current does absolutely flow through the neutral, even though the neutral is not a "current carrying" conductor.

Under normal conditions, no current flows through the ground wire. Under certain fault conditions, current does flow through the ground wire - instead of where we don't want it.

The neutral is the grounded conductor, whereas the ground is the grounding conductor.
__________________
"I want to establish in your mind very clearly that you must not think I deny all that I do not admit. On the contrary, I think there are many things which may be true, and which I shall receive as such hereafter, though I do not as yet receive them; but that is not because there is any proof to the contrary, but that the proof in the affirmative is not yet sufficient for me"
- Michael Faraday
Reply With Quote
  #6  
Old 09-17-2008, 04:22 PM
muni muni is offline
Junior Member
 
Join Date: Jul 2008
Location: hyderabad (india)
Posts: 45
Default

sir i could understand sgt wookies' and scubasteve's thread. it is very interesting and thanks for the information. but thingmaker sir thread is really some thing vague
Reply With Quote
  #7  
Old 09-17-2008, 05:19 PM
studiot's Avatar
studiot studiot is online now
E-book Developer
 
Join Date: Nov 2007
Location: Somerset UK
Posts: 3,733
Default

Depends where in the world you are.

Most mains AC electrical supply these days is three phase to the local substation. This may be a transformer on a pole near you supplying overhead cables or a transformer in a compound, with underground cables.

Three phase means that the are effectively three elctricity supplies on three separate cables.
As you know, with AC the voltage varies periodically, rising and falling with time.
The three phases are carefully controlled so that when one is rising another is falling.

On any individual phase once the current has passed through your load it is returned by your neutral connection to the substation.

Here the magic occurs, because the rises and falls in the different phases are at different times they nearly cancel each other out, leaving only a small imbalance current.

This is fed to earth at the substation.

Your neutral should not be earthed at your local distribution board as this nullifies the whole cleverness of the scheme and throws the phases into imbalance.

Steve and Wookie.

The average voltage between the phase conductor and the neutral is 230 volts standard in Europe and 120 volts standard in North America.

The voltage between any two phases is 240 volts in North America and 415 volts in Europe. So beware of suggesting that the neutral at 240 volts has no function.

The clever part of balancing the return current of one phase against another is that it substantially reduces the cabling requirement for electricity distribution.
Two common schemes are for one phase to feed alternate houses or one side of a street and another phase to feed the remainder. The third phase is used for street lighting etc.
On average the currents and thus the return currents will be very similar in each phase.

Heavy duty (industrial) equipment receives the extra oomph provided by all three phases.
Reply With Quote
  #8  
Old 09-18-2008, 12:56 PM
Metalfan1185's Avatar
Metalfan1185 Metalfan1185 is offline
Senior Member
 
Join Date: Sep 2008
Posts: 129
Default

interesting...
__________________
"There is No Knowledge that is Not Power"
Reply With Quote
  #9  
Old 09-18-2008, 01:35 PM
thingmaker3's Avatar
thingmaker3 thingmaker3 is offline
Super Moderator
 
Join Date: May 2005
Location: Rural, Oregon GMT -8
Posts: 5,072
Blog Entries: 6
Default

Quote:
Originally Posted by studiot View Post
The average voltage between the phase conductor and the neutral is 230 volts standard in Europe and 120 volts standard in North America.

The voltage between any two phases is 240 volts in North America and 415 volts in Europe. So beware of suggesting that the neutral at 240 volts has no function.
I'm not conversant with European power distribution, but American residential power is split single phase, not three phase. That's 240 between the hot leads and 120 from either hot lead to ground. American residential hot leads have current 180 degrees apart, not 120 degrees as is found in 3-phase.
__________________
"I want to establish in your mind very clearly that you must not think I deny all that I do not admit. On the contrary, I think there are many things which may be true, and which I shall receive as such hereafter, though I do not as yet receive them; but that is not because there is any proof to the contrary, but that the proof in the affirmative is not yet sufficient for me"
- Michael Faraday
Reply With Quote
  #10  
Old 09-18-2008, 09:36 PM
studiot's Avatar
studiot studiot is online now
E-book Developer
 
Join Date: Nov 2007
Location: Somerset UK
Posts: 3,733
Default

I do believe that the US has many local generating sets, especially in rural areas.
These can be of all sorts of types.

This situation is also typical in many other parts of the globe especially where population density is low.

In the UK we have centralised power stations and a distribution grid. I think they use 3 phase also because 3 is the smallest number you can connect in star - delta formation. You cannot do this with two phase systems. However the principal of load balancing on polyphase systems still holds good.
Reply With Quote
Reply   Post New Thread

Tags
, ,


Related Site Pages
Section Title
Worksheet Digital-to-Analog conversion
Worksheet Electromechanical relay logic
Textbook Harmonics in polyphase power systems : Polyphase Ac Circuits
Textbook Single-phase power systems : Polyphase Ac Circuits
Textbook ElectroStatic Discharge : Practical Analog Semiconductor Circuits
Worksheet Safety grounding
Textbook Wiring Color Codes : Color Codes
Textbook "Ladder" diagrams : Ladder Logic
Textbook pH measurement : Electrical Instrumentation Signals
Textbook Safe circuit design : Electrical Safety


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sawmill Application: Voltage concern lukas86 The Projects Forum 21 05-28-2008 10:46 PM
Ground Control anne General Electronics Chat 34 05-12-2008 11:39 PM
AC cycle how neutral stays neutral brianl General Electronics Chat 10 11-04-2007 10:19 PM
What is ground ? bhavesh96el General Electronics Chat 17 01-07-2007 04:39 AM
Neutral connection to ground direct or through an NANCYOJOJ General Electronics Chat 2 06-10-2005 06:17 PM

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 08:14 AM.


User-posted content, unless source quoted, is licensed under a Creative Commons Public Domain License.
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2014, vBulletin Solutions, Inc.